    Strange homing behavior
    908
    • Chrissundefined
      Chriss @aidar
      @aidar
      Yes, that was a setup I tried too.:
      homez.g
      G90
      M300 S800 P100
      G1 Y155 X155 F6000 ; go to first probe point
      M300 S300 P300
      M400
      M600 S800 P500
      G91               ; relative positioning
      G1 H2 Z10 F6000    ; lift Z relative to current position
      G90               ; absolute positioning
      G30               ; home Z by probing the bed
      M558 F60          ; Chriss - set the down speed
      G30
      M558 F350         ; Change the speed back
      I have exactly the same behavior, the head goes down only once and I get this error:
      Error: Z probe already triggered at start of probing move
      And "Z0" is somewhere up in the air.
      The probe config from config.g;
      M558 P1 C"zprobe.in" H5 F120 T6000
      G31 P500 X-26.0 Y-9.0 Z1.85					; Z-probe location and offset
      M557 X10:270 Y40:270 P5:5
      Edit: And the IR-Probe blinks one time during the travel to X155 X155.
      • JoergS5undefined
        JoergS5 @Chriss
        @Chriss my guess is
        I would check two things:
        I would try setting a ^ in the M558:
        M558 P1 C"^zprobe.in" H5 F120 T6000
        to activate pullup.
        In homez the second G30 at the same height means the sensor is activated immediatelly because it is still at the same height. But to find the end position you need deactivated-move-activate->found 0 position, so I would add something like:
        G1 Y155 X155 F6000
        G30
        M558 F60
        G1 H2 Z10 F6000 ; <= this Z movement here added
        G30
        M558 F350
        Chrissundefined 1 Reply Last reply Reply Quote 0
        • Chrissundefined
          Chriss @JoergS5
          @JoergS5
          Thanks for your opinion, but I guess you did not understand my text.
          The head do not goes down a second time at X155 Y155.
          The probe blink one time during the travel and a second time at the destination which ends up in the air.
          I added the G1 for testing but this did not change anything.
          I'm sooo confused, the homez.g works fine as long as it is not executed by the homeall.g.
          Cheers, Chriss
          • JoergS5undefined
            JoergS5 @Chriss
            @Chriss please see my post, I changed my answer while you answered. Please try the ^ addition.
            • Chrissundefined
              Chriss @JoergS5
              @JoergS5
              Yes.... thanks for the heads up.
              I changed (again) the M558 and added the "^".
              I simplified the homez.g a bit. This is the remaining code:
              G90
              M300 S800 P100
              M300 S300 P300
              M400
              M600 S800 P500
              G30
              With the same result, the probe get triggered up in the air. It doesn't make and difference whether I have a the "G1" you mention added or not.
              The files works fine as long as I do not call if from homeall.g.
              Btw: It is "broken" when I copy the commands into the homeall.g too.
              Cheers, Chriss
              • JoergS5undefined
                JoergS5 @Chriss
                @Chriss are you sure you have not two homez on you sdcard and take the wrong one?
                • Chrissundefined
                  Chriss @JoergS5
                  @JoergS5
                  I do not think that I can have two files with the same name in the same directory on a FAT filesystem. 😉
                  And it makes no difference whether the code is hosted directly in the homeall.g or if I execute the homez.g from the homeall.g. I still wounder about the single blink of the IR-Probe in the travel.
                  Btw: The IR Probe blinks 4 times when it starts up. I'm not sure that this is correct. I have something on top of my head that there was something like "analog mode (less than 4 blinks) with or without the pullup (^)". :?
                  • JoergS5undefined
                    JoergS5 @Chriss
                    @Chriss I didn't mean two files in the same directory, but one in sys, one in root. Please check whether you have files in your root directory...
                    • Chrissundefined
                      Chriss @JoergS5
                      @JoergS5 Guten Abend. 😉
                      Well, I think that I got your point, but this is not the case:
                      150 Here comes the directory listing.
                      drw-rw-rw- 1 ftp ftp             0 May 13 2020 gcodes
                      drw-rw-rw- 1 ftp ftp             0 May 13 2020 macros
                      drw-rw-rw- 1 ftp ftp             0 May 13 2020 sys
                      drw-rw-rw- 1 ftp ftp             0 May 13 2020 System Volume Information
                      drw-rw-rw- 1 ftp ftp             0 May 13 2020 www
                      -rw-rw-rw- 1 ftp ftp          5734 Aug 08 2018 DuetDriverFiles.zip
                      drw-rw-rw- 1 ftp ftp             0 May 12 2020 .Trash-1000
                      drw-rw-rw- 1 ftp ftp             0 May 15 2020 filaments
                      226 Transfer complete.
                      ftp>
                      I added some eyecatcher code (some extra movement) to the homez.g, I see that eyecatcher when I execute homez.g and homeall.g. So there is no other file/config involved here.
                      • JoergS5undefined
                        JoergS5 @Chriss
                        @Chriss Ebenfalls Guten Abend!
                        Sorry for my crazy ideas, I try to find the reason also...
                        I don't know a difference between running in homeall and calling a macro containing the commands. In fact, some users use homeall to put in solely three calls to the homex/y/z macros.
                        Back to the sensor: is it the Duet sensor? Do you know David's blog https://miscsolutions.wordpress.com/mini-height-sensor-board/
                        This may give some more hints.
                        • Chrissundefined
                          Chriss @JoergS5
                          @JoergS5
                          It is official now, it is snowing in hell!
                          I played a bit with that extra move.. just for fun to see where the extra blink comes up and where not bla bla....
                          So I added "G1 Y300 X300 F6000" on top of the homez.g. Again, just for fun. So the printer homes XY (0) via homeall.g and travels than to the other site of the bed. Instead of going straight to the center.
                          And you know what? It worked now 3 times in a row. I will play a bit more....
                          • Chrissundefined
                            Chriss @Chriss
                            But I still think that there is a difference between homeall.g and homez.g.
                            I have changed the homez.g a bit. I have now a "run 1" with a "G1 H1" and a little lift of that afterwards. Than the "run 2" with the "G30":
                            G90
                            M300 S800 P100
                            M300 S300 P300
                            M400
                            M600 S800 P500
                            ; Run 1
                            G1 H1 Z-500 F200 ; move Z down until the endstop is triggered
                            G1 H2 Z5 F6000    ; lift Z relative to current position
                            M400
                            ; Run 2
                            M600 S800 P2000		; beep
                            G30
                            Step one get executed whether I call homez.g or homeall.g, but "step 2" produces a:
                            WHEN I execute it via homeall.g. It works fine when I execute homez.g.
                            • JoergS5undefined
                              JoergS5 @Chriss
                              @Chriss so homeall sets some precondition which is different from when you call only homez. So need "only" shorten homeall until you find the reason...
                                How have you wired the probe?
                                Please post your full config.g
                                Do not use G1 H1. It is for endstop and negates all of the probe settings.
                                • Chrissundefined
                                  Chriss @Phaedrux
                                  @JoergS5
                                  Yes, that was my idea too, bit look at it, there is not much to remove without making it completely useless. I need a homed X and Y to move Z.
                                  @Phaedrux said in Strange homing behavior:
                                  I connected it to "zprobe.in", VCC and GND from the same connector. The ir-probe is much more user-friendly than the bl-touch. 😉
                                  I do not expect a problem with the ir-touch itself, it worked more than 99,998% if I use "homez.g"
                                  You will find it at the end.
                                  I changed the config a bit this morning. I have now:
                                  Homez.g
                                  G90
                                  M400
                                  ; Run 1
                                  M558 F250          ; Chriss - set the down speed
                                  G30
                                  ; Run 2
                                  G30
                                  And homeall.g
                                  G1 H1 X-315 Y-315 F1800 ; move quickly to X and Y axis endstops and stop there (first pass)
                                  G1 H2 X5 Y5 F6000       ; go back a few mm
                                  G1 H1 X-315 Y-315 F360  ; move slowly to X and Y axis endstops once more (second pass)
                                  M98 P"0:/sys/homez.g"
                                  config.g
                                  ; generated by RepRapFirmware Configuration Tool v2.1.8 on Sun May 10 2020 08:05:32 GMT+0200 (Central European Summer Time)
                                  G90                                            ; send absolute coordinates...
                                  M83                                            ; ...but relative extruder moves
                                  M550 P"Homer"                                  ; set printer name
                                  M552 S1                                        ; enable network
                                  M586 P0 S1                                     ; enable HTTP
                                  M586 P1 S1                                     ; enable FTP
                                  M586 P2 S1                                     ; enable Telnet
                                  M569 P0 S0                                     ; physical drive 0 goes backward
                                  M569 P1 S1                                     ; physical drive 1 goes forwards
                                  M569 P2 S1                                     ; physical drive 2 goes forwards
                                  M569 P3 S1                                     ; physical drive 3 goes forwards
                                  M584 X0 Y1 Z2:9 E3                             ; Chriss - set drive mapping two Z motors connected to driver outputs E6(9) and Z(2)
                                  M671 X-28:330 Y155:155 S5.5                    ; Chriss - leadscrews at left (connected to E6(9)) and right (connected to E2) of X axis (S=MaxCorrection)
                                  M350 E16 I0                                    ; Chriss - without interpolation
                                  M350 X16 Y16 Z16 I1                            ; Chriss - configure microstepping with interpolation
                                  M92 X80.00 Y80.16 Z400.00 E431.06              ; Chriss - set steps per mm 2560     From Bondtech: E409.51   Original: E137.81 Calulator:
        ; https://3d-druck-archiv.de/blog/grundlagen-3d-druck/steps-fuer-x-y-z-achse-einstellen-ueberpruefen-247
        ; https://selbstgedruckt.de/berechnungstools/
                                  M566 X900.00 Y900.00 Z12.00 E120.00            ; Chriss - set maximum instantaneous speed changes (mm/min)
                                  M203 X6000.00 Y6000.00 Z800.00 E1200.00        ; Chriss - set maximum speeds (mm/min) Z180
                                  M201 X500.00 Y500.00 Z20.00 E250.00            ; Chriss - set accelerations (mm/s^2)
                                  M906 X800 Y800 Z800 E800 I30                   ; set motor currents (mA) and motor idle factor in per cent
                                  M84 S30                                        ; Set idle timeout
                                  M208 X0:310 Y0:300                             ; Chriss - X carriage moves from 0 to 310, Y bed goes from 0 to 310
                                  M574 X1 S1 P"xstop"                            ; configure active-high endstop for low end on X via pin xstop
                                  M574 Y1 S1 P"ystop"                            ; configure active-high endstop for low end on Y via pin ystop
                                  M574 Z1 S2                                     ; configure Z-probe endstop for low end on Z
                                  ; Z-Probe IR Probe
                                  ; M564 S0 to disable axis limits.
                                  ;https://duet3d.dozuki.com/Wiki/Test_and_calibrate_the_Z_probe
                                  ;M557 X10:270 Y40:270 P10:10                     ; Chriss - define mesh grid
                                  ;M557 X10:270 Y40:270 P2:2
        ; https://duet3d.dozuki.com/Wiki/Gcode#Section_M557_Set_Z_probe_point_or_define_probing_grid
                                  ;; Heaters
                                  ;BED
                                  M950 H0 C"bedheat" T0                          ; create bed heater output on bedheat and map it to sensor 0
                                  M143 H0 S120                                   ; set temperature limit for heater 0 to 120C
                                  M307 H0 A245.4 C400.5 D1.3 S1.00 V24.1 B0	   ; Chriss - Disable bang-bang, tuned with "M303 H0 S80"
                                  											   ; https://duet3d.dozuki.com/Guide/Ender+3+Pro+and+Duet+Maestro+Guide+Part+4:+Calibration/40#s161
                                  M140 H0                                        ; map heated bed to heater 0
                                  ; Hotend
                                  M308 S1 P"e0temp" Y"thermistor" T100000 B4138  ; configure sensor 1 as thermistor on pin e0temp
                                  M950 H1 C"e0heat" T1                           ; create nozzle heater output on e0heat and map it to sensor 1
                                  M143 H1 S280                                   ; set temperature limit for heater 1 to 280C
                                  M307 H1 A461.2 C156.1 D3.1 S1.00 V24.0 B0		; Chriss - tuned with "M303 H1 S250"
                                  ;; Fans
                                  ; Fan for the printed part:
                                  M950 F0 C"duex.fan4" Q500                           ; create fan 0 on pin fan0 and set its frequency
                                  M106 P0 S0 H-1                                 ; set fan 0 value. Thermostatic control is turned off
                                  ; Fan for the Hotend;
                                  M950 F1 C"duex.fan3" Q500                      ; F="create fan 1" C="on pin duex.fan3" Q="and set its frequency"
                                  M106 P1 S1 H1 T45 C"Hotend"                    ; P="set fan 1" S="value" H="Thermostatic control Heater No." T=" is turned on at 45°C"
                                  ;; Tools
                                  ; Tool 0
                                  M563 P0 S"Extruder" D0 H1 F1                   ; define tool 0 (Fan F1  is bonded automatically)
                                  G10 P0 X0 Y0 Z0                                ; set tool 0 axis offsets
                                  G10 P0 R0 S0                                   ; set initial tool 0 active and standby temperatures to 0C
                                  ;; Filament Sensors - https://duet3d.dozuki.com/Wiki/Connecting_and_configuring_filament-out_sensors
                                  ; Sensor 0
                                  M591 D0 P1 C"e0_stop" S1  						; filament monitor connected to E0_stop
                                  ;; Misc
                                  ; Configure Port for the PaneDuo
                                  M575 P1 B57600 S1
                                  ;; EOF
                                    Do you have a Duex? M584 X0 Y1 Z2:9 E3 Drive 9?
                                    If so, you may want to define it here:
                                    M350 E16 I0 No interpolation for the poor extruder?
                                    The M140 must come before the M143 for your bed heater.
                                    ;BED
                                    M600 isn't a beep. It's a filament change pause.
                                    https://duet3d.dozuki.com/Wiki/Gcode#Section_M600_Filament_change_pause
                                    ; Run 2
                                    G30
                                    You'd want M300
                                    https://duet3d.dozuki.com/Wiki/Gcode#Section_M300_Play_beep_sound
                                    I'm actually wondering if some of your comments are being parsed strangely. The forum code block gets pretty confused by them as you can see, but when I copied and pasted it into a text editor with gcode highlighting it detected the comments ; correctly. Not sure how the Duet gcode parser could be handling it. Might be worth cleaning up your comments to be rather minimal particularly in the area where the URLs are.
                                    Can you send M558 P1 and G31 and see if it echoes back the same values as in config.g?
                                    • Chrissundefined
                                      Chriss @Phaedrux
                                      Indeed, I have one and it is connected. 😉
                                      Added
                                      I had some strange behaviors in the past with the original extruder. That may be different now with the bondtech. Well, I added it. Lets see later how that works now.
                                      Done!
                                      You are right, my bad. I wanted to change the frequency, which ended in the "double comand" and not "double frequency". Typo, I removed all of the beeps in the meantime anyway. They where for debug only anyway.
                                      Indeed, that is a very good idea. I removed all the URLs and removed other things like "°". Just in case, that would not be the first time that I have bombed a parser with unexpected characters. 😉
                                      Update:
                                      I tested/played a bit with the setup to understand the behavior better.
                                      Let me describe it like that: The "homeall.g" seems to work from time to time when "z" is not far away from the bed surface. But sometimes it drives into the bed.
                                      It seems that it gets triggered in the air only when "z" is more than 10cm away from the bed when I power on the printer. It works or drives into the bed when the head is below 5cm away from the bed.
                                      Did it make myself clear?
                                      Does that makes any sense to you?
                                      Cheers, Chriss
                                        I thought we would at elast get something back from M558 P1.
                                        Please try sending the full M558 command from your config.g in the console.
                                        I can't remember if I asked before, but can you send M98 P"config.g" and see what you get for errors and messages?
                                        • Chrissundefined
                                          Chriss @Phaedrux
                                          I did not fully understand what you mean. 😞 I added "M558 P1" at the end of config.g, without any result. I do not see any output of that, nowhere.
                                          I tried telnet:
                                          [chriss@leela ~]$ telnet 192.168.1.170
                                          Trying 192.168.1.170...
                                          Connected to 192.168.1.170.
                                          Escape character is '^]'.
                                          M558 P1
                                          ok
                                          I guess that you mean "M98 P"0:/sys/config.g""
                                          HTTP is enabled on port 80
                                          FTP is enabled on port 21
                                          TELNET is enabled on port 23
                                          Warning: Heater 0 appears to be over-powered. If left on at full power, its temperature is predicted to reach 270C
                                          Warning: Heater 1 appears to be over-powered. If left on at full power, its temperature is predicted to reach 486C
                                          ok
                                          So no parsing error if you where aiming for that.
                                          Cheers, Chriss
                                            I mean send this in the console
                                            And then try your homing.
                                            Though I'm starting to wonder if it's something wrong with the IR probe itself.