Tool board - no response
-
@barbarossa-cologne M122 B121
Diagnostics for board 121:
Duet TOOL1LC firmware version 3.3 (2021-06-15 16:12:58)
Bootloader ID: not available
Never used RAM 3636, free system stack 2789 words
Tasks: Move(notifyWait,0.0%,153) HEAT(delaying,0.1%,117) CanAsync(notifyWait,0.0%,65) CanRecv(notifyWait,0.0%,76) CanClock(notifyWait,0.0%,65) TMC(delaying,2.9%,57) MAIN(running,92.1%,350) IDLE(ready,0.0%,41) AIN(delaying,4.9%,142), total 100.0%
Last reset 00:03:41 ago, cause: software
Last software reset data not available
Driver 0: position 0, 409.0 steps/mm, standstill, SG min/max 0/0, read errors 0, write errors 1, ifcnt 61, reads 45026, writes 13, timeouts 0, DMA errors 0, steps req 0 done 0
Moves scheduled 0, completed 0, in progress 0, hiccups 0, step errors 0, maxPrep 0, maxOverdue 0, maxInc 0, mcErrs 0, gcmErrs 0
Peak sync jitter 0/9, peak Rx sync delay 208, resyncs 0/0, no step interrupt scheduled
VIN: 24.1V
MCU temperature: min 38.4C, current 38.5C, max 38.8C
Ticks since heat task active 186, ADC conversions started 220384, completed 220383, timed out 0, errs 0
Last sensors broadcast 0x00000002 found 1 191 ticks ago, loop time 0
CAN messages queued 2487, send timeouts 0, received 1957, lost 0, free buffers 37, min 37, error reg 0
dup 0, oos 0/0/0/0, bm 0, wbm 0, rxMotionDelay 0
Accelerometer detected: no
I2C bus errors 4619, naks 4619, other errors 4619 -
Can you send m98 p"config.g" and post the results?
Do you have your other tool boards connected as well?
-
@phaedrux
I don´t have the other connected, yet.Error: Response timeout: CAN addr 123, req type 6027, RID=96
Error: Fan number 5 not found
Error: in file macro line 82 column 13: M106: expected number after 'H'
11.8.2021, 22:44:22 Error: Response timeout: CAN addr 123, req type 6027, RID=94
Error: Fan number 4 not found
11.8.2021, 22:44:20 Error: Response timeout: CAN addr 122, req type 6027, RID=90
Error: Fan number 2 not found
Error: Response timeout: CAN addr 122, req type 6027, RID=92
Error: Fan number 3 not found
11.8.2021, 22:44:16 Error: Response timeout: CAN addr 123, req type 6026, RID=82
Error: Heater 3 not found
Error: Heater 3 does not exist
11.8.2021, 22:44:14 Error: Response timeout: CAN addr 122, req type 6043, RID=68
Response timeout: CAN addr 123, req type 6043, RID=69
Error: bad grid definition: X range too small
Error: Response timeout: CAN addr 122, req type 6031, RID=76
Error: Response timeout: CAN addr 122, req type 6026, RID=78
Error: Heater 2 not found
Error: Heater 2 does not exist
Error: Response timeout: CAN addr 123, req type 6031, RID=80
11.8.2021, 22:44:06 Error: Response timeout: CAN addr 122, req type 6042, RID=64
Response timeout: CAN addr 123, req type 6042, RID=65
11.8.2021, 22:44:04 Error: Response timeout: CAN addr 122, req type 6042, RID=60
Response timeout: CAN addr 123, req type 6042, RID=61
11.8.2021, 22:44:02 Error: Response timeout: CAN addr 122, req type 6042, RID=56
Response timeout: CAN addr 123, req type 6042, RID=57
11.8.2021, 22:44:00 Error: Response timeout: CAN addr 123, req type 6018, RID=53
Driver assignments: X1.1 Y0.0:0.1 Z0.2:0.3:0.4:0.5 E121.0:122.0:123.0, 3 axes visible
11.8.2021, 22:43:59 m98 p"config.g"
Error: Response timeout: CAN addr 122, req type 6018, RID=52 -
@barbarossa-cologne
Hot end fan is running.
Print cooling fan is not running.
I can´t control both. -
How is the PT1000 connected?
Is it actually a PT1000?Photos of your toolboard wiring?
-
@phaedrux
It's the original tool changer thermistor.
Is it a pt100?
Oh no... -
-
@barbarossa-cologne
-
@barbarossa-cologne I've seen that crazy temperature value once before when a tool board was configured for a PT1000 sensor but the sensor wasn't connected.
-
@dc42 that's what I checked another time 2 minutes ago. It's definitely connected.
-
@barbarossa-cologne have you measured its resistance, to verify that it is a PT1000, not a PT100 or a thermistor?
-
@dc42 connected a different thermistor = same problem
-
@dc42
Yes. Now I connected a typical Chinese thermistor and it shows the same number for temperature:/ -
@barbarossa-cologne the config.g file you posted was for a PT1000, not a thermistor. Specifically, this line:
M308 S1 P"121.temp0" Y"pt1000" R2200 ; configure sensor 1 as PT1000 on pin 121.temp0
-
@dc42
Eeeehm ok.
Yes
That was the problem...
SOLVED
thanks a lot