    Z motor on expansion board not moving
    1.8k
      Can you gather a M122 report for the mainboard and the expansion board?
      Can you also send M98 P"config.g" and report any errors?
      So you have your Z axis split between the mainboard and expansion board? Would make more sense to try and keep all of Z on a single board.
      M584 X0.1 Y0.2 Z0.3:0.4:0.5:1.2 E0.1
      You also appear to be trying to map 0.1 driver to both X and E
      wdenkerundefined 1 Reply Last reply Reply Quote 0
      • wdenkerundefined
        wdenker @Phaedrux
        @Phaedrux said in Z motor on expansion board not moving:
        M98 P"config.g"
        www.bd3dcustoms.com | BD3DCUSTOMS Supercube
        • wdenkerundefined
          wdenker @wdenker
          @Phaedrux almost looks like it isn't recognizing the expansion board driver. Since it isn't showing any of those drivers.
          M122
          RepRapFirmware for Duet 3 MB6HC version 3.4.6 (2023-07-21 14:11:38) running on Duet 3 MB6HC v1.02 or later (standalone mode)
          Board ID: 08DJM-9P63L-DJ3T8-6J1DA-3SN6J-KV7VA
          Used output buffers: 2 of 40 (25 max)
          Static ram: 153252
          Dynamic ram: 98808 of which 44 recycled
          Never used RAM 98496, free system stack 154 words
          Tasks: NETWORK(ready,79.2%,172) ETHERNET(notifyWait,0.4%,400) HEAT(notifyWait,0.0%,321) Move(notifyWait,0.0%,261) CanReceiv(notifyWait,0.0%,773) CanSender(notifyWait,0.0%,335) CanClock(delaying,0.0%,347) TMC(notifyWait,18.9%,90) MAIN(running,1.5%,925) IDLE(ready,0.0%,30), total 100.0%
          Owned mutexes:
          Last reset 02:43:12 ago, cause: software
          Last software reset at 2023-12-20 12:26, reason: User, GCodes spinning, available RAM 98572, slot 2
          Software reset code 0x0003 HFSR 0x00000000 CFSR 0x00000000 ICSR 0x0044a000 BFAR 0x00000000 SP 0x00000000 Task MAIN Freestk 0 n/a
          Error status: 0x00
          Step timer max interval 662
          MCU temperature: min 32.4, current 33.8, max 34.0
          Supply voltage: min 24.0, current 24.1, max 24.2, under voltage events: 0, over voltage events: 0, power good: yes
          12V rail voltage: min 12.1, current 12.3, max 12.5, under voltage events: 0
          Events: 750 queued, 750 completed
          Driver 0: standstill, SG min 0, mspos 880, reads 364, writes 17 timeouts 0
          Driver 1: standstill, SG min 0, mspos 536, reads 333, writes 48 timeouts 0
          Driver 2: standstill, SG min 0, mspos 200, reads 334, writes 48 timeouts 0
          Driver 3: standstill, SG min 0, mspos 752, reads 350, writes 32 timeouts 0
          Driver 4: standstill, SG min 0, mspos 752, reads 350, writes 32 timeouts 0
          Driver 5: standstill, SG min 0, mspos 752, reads 350, writes 32 timeouts 0
          Date/time: 2023-12-20 15:10:08
          Slowest loop: 8.18ms; fastest: 0.05ms
          === Storage ===
          Free file entries: 10
          SD card longest read time 2.5ms, write time 0.0ms, max retries 0
          DMs created 125, segments created 3, maxWait 133200ms, bed compensation in use: none, comp offset 0.000
          === MainDDARing ===
          Scheduled moves 22, completed 22, hiccups 0, stepErrors 0, LaErrors 0, Underruns [0, 0, 0], CDDA state -1
          === AuxDDARing ===
          Bed heaters 0 -1 -1 -1 -1 -1 -1 -1 -1 -1 -1 -1, chamber heaters -1 -1 -1 -1, ordering errs 0
          Segments left: 0
          Movement lock held by null
          HTTP is idle in state(s) 0
          Telnet is idle in state(s) 0
          File is idle in state(s) 0
          USB is idle in state(s) 0
          Aux is idle in state(s) 0
          Trigger is idle in state(s) 0
          Queue is idle in state(s) 0
          LCD is idle in state(s) 0
          SBC is idle in state(s) 0
          Daemon is idle in state(s) 0
          Aux2 is idle in state(s) 0
          Code queue is empty
          === Filament sensors ===
          Extruder 0 sensor: ok
          === CAN ===
          Messages queued 88159, received 117537, lost 0, boc 0
          Longest wait 1ms for reply type 6018, peak Tx sync delay 385, free buffers 50 (min 49), ts 48961/48960/0
          Tx timeouts 0,0,0,0,0,0
          === Network ===
          Slowest loop: 3.23ms; fastest: 0.03ms
          Responder states: HTTP(0) HTTP(0) HTTP(0) HTTP(0) HTTP(0) HTTP(0) FTP(0) Telnet(0) Telnet(0)
          HTTP sessions: 1 of 8
          = Ethernet =
          State: active
          Error counts: 0 0 0 1 0 0
          Socket states: 5 2 2 2 2 2 0 2
          = WiFi =
          Interface state: disabled
          Module is disabled
          === Multicast handler ===
          Responder is inactive, messages received 0, responses 0
            jay_s_uk @wdenker
            @wdenker send M122 Box where X is the CAN address of the expansion board
            • wdenkerundefined
              wdenker @jay_s_uk
              @jay_s_uk said in Z motor on expansion board not moving:
              M122 Box
              M122 B1
              Diagnostics for board 1:
              Duet EXP3HC rev 1.02 or later firmware version 3.4.6 (2023-07-21 14:15:46)
              Bootloader ID: SAME5x bootloader version 2.4 (2021-12-10)
              All averaging filters OK
              Never used RAM 158600, free system stack 192 words
              Tasks: Move(notifyWait,0.0%,162) HEAT(notifyWait,0.0%,88) CanAsync(notifyWait,0.0%,69) CanRecv(notifyWait,0.0%,82) CanClock(notifyWait,0.0%,71) TMC(notifyWait,7.3%,99) MAIN(running,91.4%,411) IDLE(ready,0.0%,40) AIN(delaying,1.3%,263), total 100.0%
              Last reset 03:19:24 ago, cause: software
              Last software reset data not available
              Driver 0: pos 0, 80.0 steps/mm,standstill, SG min n/a, mspos 8, reads 63513, writes 0 timeouts 0, steps req 0 done 0
              Driver 1: pos 0, 80.0 steps/mm,standstill, SG min n/a, mspos 8, reads 63513, writes 0 timeouts 0, steps req 0 done 0
              Driver 2: pos 0, 160.0 steps/mm,standstill, SG min n/a, mspos 16, reads 63513, writes 0 timeouts 0, steps req 0 done 0
              Moves scheduled 0, completed 0, in progress 0, hiccups 0, step errors 0, maxPrep 0, maxOverdue 0, maxInc 0, mcErrs 0, gcmErrs 0
              Peak sync jitter -4/7, peak Rx sync delay 181, resyncs 2/1, no step interrupt scheduled
              VIN voltage: min 24.3, current 24.3, max 24.4
              V12 voltage: min 12.3, current 12.3, max 12.3
              MCU temperature: min 29.8C, current 30.7C, max 31.3C
              Last sensors broadcast 0x00000000 found 0 105 ticks ago, 0 ordering errs, loop time 0
              CAN messages queued 24829, send timeouts 14, received 18460, lost 0, free buffers 37, min 37, error reg 320000
              Last cancelled message type 4519 dest 0
              dup 0, oos 0/0/0/0, bm 0, wbm 0, rxMotionDelay 0
                jay_s_uk @wdenker
                @wdenker I can see the error in your config for M584. For z on the expansion board you should use the address and driver number which in this case would be Z1.0:1.1:1.2 (assuming you're using all 3)
                • wdenkerundefined
                  wdenker @jay_s_uk
                  @jay_s_uk I don't see any error in my M584 I also just ran another M98 P"config.g"
                  M584 X0.1 Y0.2 Z0.3:0.4:0.5:1.2 E0.0
                  M98 P"config.g"
                  HTTP is enabled on port 80
                  FTP is enabled on port 21
                  TELNET is enabled on port 23
                  Error: Driver 1.2 does not exist
                  Error: Sensor number out of range
                    jay_s_uk @wdenker
                    @wdenker so a couple of things. You need to have something like G4 S2 in your config before any CAN boards are referenced to give them time to connect. So put it before the M584.
                    You have M584 twice in your config.
                    • wdenkerundefined
                      wdenker @jay_s_uk
                      @jay_s_uk G4 S2 is at the very first of the config.g M584 is called twice as we were having some issues and testing a theory. I can remove those no problem. Doesn't explain why it says driver 1.2 doesn't exist even though it is definitely there.
                        jay_s_uk @wdenker
                        @wdenker G4 S2 isn't in the config you posted in the first post. In which case repost your config please ideally as code like your M122 outputs so I don't have to download it to look at it
                        • wdenkerundefined
                          wdenker @jay_s_uk
                          @jay_s_uk
                          ; generated by RepRapFirmware Configuration Tool v3.4.5 on Thu Jun 18 2020 20:04:02 GMT-0600 (Mountain Daylight Time)
                          G4 S2
                          G90                                                  ; send absolute coordinates...
                          M83                                                  ; ...but relative extruder moves
                          M550 P"Fabricator by IOFX"                               ; set printer name
                          M669 K1                                              ; select CoreXY mode
                          M552 P192.168.1.14 S1                                     ; enable network and acquire dynamic address via DHCP
                          M586 P0 S1                                           ; enable HTTP
                          M586 P1 S1                                           ; enable FTP
                          M586 P2 S1                                           ; enable Telnet
                          M584 X0.1 Y0.2 Z0.3:0.4:0.5:1.2 E0.0                 ; set drive mapping
                          M569 P0.0 S1                                         ; physical drive 0.0 goes backwards
                          M569 P0.1 S0                                         ; physical drive 0.1 goes backwards
                          M569 P0.2 S1                                         ; physical drive 0.2 goes backwards
                          M569 P0.3 S1                                         ; physical drive 0.3 goes forwards
                          M569 P0.4 S1                                         ; physical drive 0.3 goes forwards
                          M569 P0.5 S1                                         ; physical drive 0.3 goes forwards
                          M569 P1.0 S1                                         ; physical drive 1.0 goes backwards
                          M569 P1.1 S1                                         ; physical drive 1.1 goes backwards
                          M569 P1.2 S1                                        ; physical drive 1.2 goes backwards
                          M915 P0.1:0.2 F0 S2
                          M350 X16 Y16 Z8 E8 I1                              ; configure microstepping with interpolation
                          M92 X160.00 Y160.00 Z160.00 E420.00                    ; set steps per mm
                          M205 X20.00 Y20.00 Z3.00 E120.00                  ; set maximum instantaneous speed changes (mm/min)
                          M203 X12000.00 Y12000.00 Z300.00 E6000.00              ; set maximum speeds (mm/min)
                          M201 X2500.00 Y2500.00 Z100.00 E10000.00             ; set accelerations (mm/s^2)
                          M906 X1600 Y1600 Z1800 E1600 I30                         ; set motor currents (mA) and motor idle factor in per cent
                          M84 S30                                              ; Set idle timeout
                          M671 X-125:-125:1125:1125 Y100:900:900:100 S7            ; leadscrews at left (connected to Z) and right (connected to E1) of X axis
                          M208 X0 Y0 Z0 S1                                     ; set axis minima
                          M208 X1000 Y1000 Z1100 S0                               ; set axis maxima
                          M574 X1 S3 F0 R0                                          ; configure sensorless endstop for low end on X
                          M574 Y1 S3 F0 R0                                          ; configure sensorless endstop for low end on Y
                          M574 X1 Y1 S3                               ; Set endstops controlled by motor load detection
                          M574 Z1 S2                                           ; configure Z-probe endstop for low end on Z
                          M915 X Y S2 R0 F0 	                    ; set X and Y to sensitivity 7, do nothing when stall, unfiltered
                          M950 S0 C"io7.out"                           ; create servo pin 0 for BLTouch
                          M558 P9 C"^io7.in" H5 F120 T6000             ; set Z probe type to bltouch and the dive height + speeds
                          G31 P500 X0 Y0 Z2.65                          ; set Z probe trigger value, offset and trigger height
                          M557 X25:955 Y25:955 S150                             ; define mesh grid
                          M308 S0 P"temp1" Y"thermistor" T100000 B4725          ; configure sensor 0 as thermistor on pin temp1
                          M950 H0 C"out1" T0                                   ; create bed heater output on out1 and map it to sensor 0
                          M307 H0 B1 S1.00                                     ; enable bang-bang mode for the bed heater and set PWM limit
                          M140 H0                                              ; map heated bed to heater 0
                          M143 H0 S120                                         ; set temperature limit for heater 0 to 120C
                          M308 S1 P"temp2" Y"pt1000"                           ; configure sensor 1 as thermistor on pin temp0
                          M950 H1 C"out2+out3" T1                                   ; create nozzle heater output on out0 and map it to sensor 1
                          M307 H1 B0 S1.00                                     ; disable bang-bang mode for heater  and set PWM limit
                          M950 F0 C"out8" Q500                               ; create fan 0 on pin out6 and set its frequency
                          M106 P0 S0 H-1 C"Part Cooling"                                       ; set fan 0 value. Thermostatic control is turned off
                          M950 F1 C"out9" Q500                               ; create fan 0 on pin out6 and set its frequency
                          M106 P1 S0 H-1 C"Part Cooling"                                       ; set fan 0 value. Thermostatic control is turned off
                          M950 F2 C"out7" Q500                                ; create fan 1 on pin out7 and set its frequency
                          M106 P2 S1 H1 T45                                    ; set fan 1 value. Thermostatic control is turned on
                          M950 F5 C"1.out6" Q500                                 ; create fan 1 on pin out7 and set its frequency
                          M106 P5 S1 H100 T15                                    ; set fan 1 value. Thermostatic control is turned on
                          M950 F3 C"1.out7" Q500                                 ; create fan 1 on pin out7 and set its frequency
                          M106 P3 S1 H100 T15                                    ; set fan 1 value. Thermostatic control is turned on
                          M950 F4 C"1.out8" Q500                                 ; create fan 1 on pin out7 and set its frequency
                          M106 P4 S1 H100 T15                                    ; set fan 1 value. Thermostatic control is turned on
                          M563 P0 D0 H1 F0:1                                     ; define tool 0
                          G10 P0 X0 Y0 Z0                                      ; set tool 0 axis offsets
                          G10 P0 R0 S0                                         ; set initial tool 0 active and standby temperatures to 0C
                          M591 D0 P2 C"io1.out" S1 ; filament monitor connected to E0 endstop
                          M911 S22 R23.5 P"M913 X0 Y0 G91 M83 G1 Z3 E-5 F1000" ; set voltage thresholds and actions to run on power loss
                          M570 H1 P10 T15 S999
                          M501;
                            jay_s_uk @wdenker
                            @wdenker I guess it doesn't like the Z drivers being spread across the mainboard and CAN board. Best move all Z drivers on to one and move Z or Y onto the 3HC
                            • wdenkerundefined
                              wdenker @jay_s_uk
                              @jay_s_uk any ideas on the filament error I get literally every 30 seconds no matter no filament movement?
                              • wdenkerundefined
                                wdenker @wdenker
                                @wdenker can't even get it to report 3 out of 4 times.
                                12/20/2023, 4:25:15 PM	M591 D0
                                12/20/2023, 4:25:12 PM	M591 D0
                                Simple filament sensor on pin (io1.out,serial1.tx), enabled, output high when no filament, filament present: no
                                12/20/2023, 4:25:00 PM	M591 D0
                                12/20/2023, 4:24:59 PM	M591 D0
                                12/20/2023, 4:24:41 PM	M591 D0
                                  jay_s_uk @wdenker
                                  @wdenker it probably needs connecting to a .in rather than a .out
                                  • wdenkerundefined
                                    wdenker @jay_s_uk
                                    @jay_s_uk we've tried both in and out.
                                      jay_s_uk @wdenker
                                      @wdenker can you confirm your wiring, ideally with pictures , and what type of filament sensor it is?
                                      wdenkerundefined 2 Replies Last reply Reply Quote 0
                                      • wdenkerundefined
                                        wdenker @jay_s_uk
                                        @jay_s_uk ah you were right. We had to switch it to 5v vs 3.3 and didn't have it on in after we swapped to the 5v. So all of my issues are resolved at this point.
                                        wdenkerundefined 1 Reply Last reply Reply Quote 1
                                        • wdenkerundefined
                                          wdenker @wdenker
                                          @wdenker Well I got ahead of myself still getting the error just not as often.
                                          • wdenkerundefined
                                            wdenker @jay_s_uk
                                            @jay_s_uk Here are the pics. I have also updated config to reflect going to io2.in vs out PXL_20231220_234947688.jpg PXL_20231220_234959902.jpg