      Update from today - is that I thought I have updated the firmware on the Mini5+ board yesterday - but actually there was a timeout and it didn't update.
      I could check the firmware etc. and run other commands - but firmware updates wouldn't work
      The main 6HC board was on 3.5.4 and the Mini5+ on 3.4.0.
      I spent most of the morning checking cables and making up two more cables - which I tried running from the tool expansion board but still got the same error.
      Eventually though I figured out the problem - which was related to 3.4.0 not seeming to like being updated via CAN-FD
      So I manually upgraded the Mini5+ board via SD card and usb terminal to 3.5.1 - and downgraded the main system - and all was then ok.
      I then upgraded them both to 3.5.4 and they worked ok.
      Motors for first gantry now all connected up - and X,Y & Z movement now working.
      Mains Heatbed basic function also working. I had forgotten to install the in power initially - but figured it out after a while. Will have to do PID tuning at some point.
      I was going to configure sensorless homing next - but based on the Duet documentation mentioning how inaccurate that method is I think I will add some limit switches and use them instead for the homing.
        dc42 administrators @dwuk3d
        @dwuk sensorless homing isn't as good as homing with a limit switch, but it's OK if you don't need the facility to resume a print that has been interrupted due to power failure. I still use sensorless homing for the X and Y axes of my tool changer.
        dwuk3dundefined 1 Reply Last reply Reply Quote 0
        • dwuk3dundefined
          dwuk3d @dc42
          @dc42 Thanks - Will get the printer working on Sensorless first as you suggest and leave looking into limit switches until a bit later.
          Update: Got X and Y Sensorless homing working in about 10 mins - its much easier to do than it was on Klipper.
          o_lampeundefined 1 Reply Last reply Reply Quote 1
          • o_lampeundefined
            o_lampe @dwuk3d
            @dwuk Sensorless homing will do for now, but with more and more toolheads involved you'll need perfect homing positions relative to each other.
            Otherwise it'll look like that:
            dc42undefined dwuk3dundefined 2 Replies Last reply Reply Quote 0
              dc42 administrators @o_lampe
              @o_lampe good point, I'd forgotten that it was an IDEX machine.
              • dwuk3dundefined
                dwuk3d @o_lampe
                @o_lampe Agreed - I would if possible like to include auto head alignment in the design - so it could work in that case I suppose if you auto align every time you power on, or for every print.
                The other issue is the fact that after quite a few goes at trying to get sensorless homing working on the 2nd Gantry (the U & V axis) I have found out that it doesn't work on Mini5+'s used as a tool board - even with the latest 3.6 firmware.
                So will add switches for U&V initially, and eventually X&Y too.
                jay_s_ukundefined droftartsundefined dc42undefined 3 Replies Last reply Reply Quote 0
                  jay_s_uk @dwuk3d
                  @dwuk that's one for @dc42 to look at then with sensorless homing on CAN boards being a new feature
                    droftarts administrators @dwuk3d
                    @dwuk said in Sovol SV08 Multiple Motion System Upgrade.:
                    I thought the 3.6.0-beta.3 release had it partially working on the Mini5+ as-expansion, possibly only on drivers 0, 1 and 5. I’ve been testing this, and @dc42 has supplied me with fixed firmware that fully works. Let me know if you would like to try it.
                      There's a build at https://www.dropbox.com/scl/fo/bx70c7u0bshq79ez83mnn/AKMj4UCEimtQuGYxRj_d0ew?rlkey=7yiq3x5fcae3v2ogslfocx1op&dl=0 in which this is fixed.
                      • dwuk3dundefined
                        dwuk3d @dc42
                        @dc42 Thanks will try that out this afternoon - will use sensorless just for testing purposes - and move over to switches at some point.
                        • dwuk3dundefined
                          dwuk3d
                          Good progress made on wiring up first extruder.
                          Main issues I faced were:
                          1. Sizes of connectors - 95% of the Sovol connectors are tiny 1.25mm Female, and most of the Duet are 2mm Female. So made up some adaptors 1.25mm Male to 2mm Female - found a nice kit with pre-crimped 1.25mm wires and sockets and plugs.
                          Didn't want to cut off existing connectors as may want to go back, plus wires a bit short to reach board too.
                          1. Inductive Probe 24V power - ended up splicing in an extra plug on the VIN power feed - but not ideal as it means two plugs to disconnect
                          2. Blower fans - The extruder has two - one of which is 3 pin and the other 2 pin - so wired them together, and - with VOUT and Tacho In on Out_2. and GND from unused IO1.
                          3. Heater power is a 2mm Female - whereas the 1LC is a screw connector. Didn't have any 2 way Male Sockets - so cut down 5 way temporarily - have order some pre-crimped from the same place as the 1.25mm ones as a more permanent solution. Also had trouble getting the crimped cable to fit into the screw connector.
                          Overall though - ready for a test this afternoon.
                          Wiring still a bit messy - and adaptors longer than they need to be - but not 100% where I am going to end up placing the 1LC board - so left them long for now.
                          0466238B-41BA-46A1-8B65-8F9E8F856DC7.jpeg A6BB9C7C-8480-4FDB-8BE4-52D1A4F30ADB_1_102_o.jpeg
                          • dwuk3dundefined
                            dwuk3d @dc42
                            @dc42 Thanks tried firmware but couldn't get it to work. I got a message about changing to StealthChop - which I did for the two drivers on the Mini5+ - everything else is on Spreadcycle.
                            Then it just kept saying that my speed was either too fast or too slow.
                            Reread the documentation here a few times - but can't really figure out what I need to change to get it to work.
                            Current relevant settings are:
                            ; Smart Drivers
                            M569 P0.0 S1 D2 ; driver 0.0 goes forwards (Z axis)
                            M569 P0.1 S1 D2 ; driver 0.1 goes forwards (Z axis)
                            M569 P0.2 S0 D2 ; driver 0.2 goes backwards (Z axis)
                            M569 P0.3 S1 D2 ; driver 0.3 goes forwards (X axis)
                            M569 P0.4 S0 D2 ; driver 0.4 goes backwards (Y axis)
                            M569 P0.5 S0 D2 ; driver 0.5 goes backwards (Z axis)
                            M569 P1.0 S0 D3 V2000 ; driver 1.0 goes backwards (U axis)
                            M569 P1.1 S0 D3 V2000 ; driver 1.1 goes backwards (V axis)
                            M569 P121.0 S1 D2 ; driver 121.0 goes forwards (extruder 0)
                            ; Motor Idle Current Reduction
                            M906 I30 ; set motor current idle factor
                            M84 S30 ; set motor current idle timeout
                            ; Axes
                            M584 X0.3 Y0.4 Z0.1:0.2:0.0:0.5 U1.0 V1.1 ; set axis mapping
                            M350 X16 Y16 Z16 U16 V16 I1 ; configure microstepping with interpolation
                            M906 X800 Y800 Z800 U800 V800 ; set axis driver currents
                            M92 X80 Y80 Z533.33 U80 V80 ; configure steps per mm
                            M208 X0:200 Y0:200 Z0:200 U0:200 V0:200 ; set minimum and maximum axis limits
                            M566 X900 Y900 Z12 U900 V900 ; set maximum instantaneous speed changes (mm/min)
                            M203 X6000 Y6000 Z180 U6000 V6000 ; set maximum speeds (mm/min)
                            M201 X500 Y500 Z20 U500 V500 ; set accelerations (mm/s^2)
                            M574 X2 S3 ; configure X axis endstop
                            M574 Y1 S3 ; configure Y axis endstop
                            M574 Z1 S4 ; configure Z axis endstop
                            M574 U2 S3 ; configure U axis endstop
                            M574 V1 S3 ; configure V axis endstop
                            ; Custom settings
                            M915 X Y U V R0 F0
                            ; homeu.g
                            ; called to home the U axis
                            ; generated by RepRapFirmware Configuration Tool v3.5.10 on Thu Jan 23 2025 15:02:10 GMT+0000 (Greenwich Mean Time)
                            M913 U40 V40
                            M400
                            ; increase Z
                            G91 ; relative positioning
                            G1 H2 Z5 F12000 ; move Z relative to current position to avoid dragging nozzle over the bed
                            G90 ; absolute positioning
                            ; home U
                            var maxTravel = move.axes[0].max - move.axes[0].min + 5 ; calculate how far X can travel plus 5mm
                            G1 H1 U{var.maxTravel} F2000 ; coarse home in the +U direction
                            G1 U-5 F6000 ; move back 5mm
                            G1 H1 U{var.maxTravel} F700 ; fine home in the +U direction
                            ; decrease Z again
                            G1 H2 Z-5 F6000 ; move Z relative to current position
                            M400
                            M913 U100 V100
                            M400
                              @dwuk please read https://docs.duet3d.com/en/User_manual/Connecting_hardware/Sensors_stall_detection. The TMC2209 drivers on the Mini5+ are quite finicky as regards getting stall detection to work. You need to at least reduce the M569 V parameter to a lower value (at least during stall homing) to avoid the "too slow" error message,
                              • o_lampeundefined
                                o_lampe @dwuk3d
                                Mirror or copy mode should work OK, but optical sensors are the best.
                                • dwuk3dundefined
                                  dwuk3d
                                  Progress update.
                                  Upgraded Axis with proper Pulley Posts and Proper Linear Rail Carriage on the UV gantry.
                                  Just need to upgrade UV gantry pulley posts.
                                  The 5mm linear rail for the pulley posts was pretty hard to cut - had to use angle grinder.
                                  All Axis working and Homing working on X,Y & Z.
                                  I will pursue getting sensorless homing working on U & V - but will also install switches or optional sensors on X,Y,U & V before going too much further.
                                  Z Inductive probe working with logic shifter - but waiting to see if there is a better solution.
                                  Heated bed, Extruder and 2 of 3 fans all working - but I haven't done any heater tuning yet.
                                  Next step tomorrow is to work out how to do Z Offets - as I followed the commissioning instructions - but it keeps setting Z to zero at the trigger height.
                                  Will then do some distance and extrusion length calibration before hopefully trying my first print on the XYZ gantry tomorrow.
                                  Next step after that and end stops is the upgrades to the 2nd Extruder on the UV gantry - which is currently still connected to the Klipper board. IMG_6630.JPG
                                  • o_lampeundefined
                                    o_lampe @dwuk3d
                                    @dwuk One thing I noticed in an earlier picture was some scratching belts:
                                    I thought it was just temporary, but it still seems a problem.
                                    • dwuk3dundefined
                                      dwuk3d @o_lampe
                                      @o_lampe Well spotted - yes it is due to the extra IDEX carriage I left on the rear gantry.
                                      If I take off the plastic coupler from the carriage there is a risk of the carriage falling off the end of the rail and I think it is that which is clashing with the belts.
                                      For the IDEX phase I am going to need to move the pulley positions slightly forward to avoid the problem you spotted - but in the meantime I don't think it is causing any great issues other than limiting travel - but will find out when I do some more testing.
                                      I am starting to think about Reprap IDEX kinematics -
                                      I was pleasantly surprised to find that CoreXYUV seems to support two CoreXY gantries ok - but for IDEX on top of CoreXYUV I think I am going to have to work out how you define completely new Kinematics (if thats possible) otherwise it is going to end up with loads more fairly complicated post-processing.
                                      I think what I would really need is to be able to have an X and 'x' axis for each gantry that I can specify both coordinates for in G0-G3 commands (or Macro replacements) I.e. For mirror mode / duplicate mode etc.- Rather than using a command to change the mode between Toolchange/Duplicate and Mirror - it should be fairly easy to work out and send two X coordinates in the same G0-G3 command to achieve the desired effect.
                                      So what I will be looking for is something like CoreXxYUuV for dual gantry IDEX.
                                      With .Zabcd - for the Z hoppers, and then finally. CoreXxYUuVy - for the occasionally moving bed phase (5).
                                      My current thinking on IDEX too is that I will stick with the Ratrig VCore4 approach of two extra Y motors per gantry initially (although it would be nice to reduce this down to one extra per ganty) - but I think I will try putting them at the front rather than the back to help balance the weight on my flying gantries.
                                      • dwuk3dundefined
                                        dwuk3d @dc42
                                        @dc42 Have spent a fair bit of time trying to get this sensorless homing on the tool board Mini5+ to work - I reduced V right down to 100 - but I still can't get it to accept a speed - it just keeps saying too slow or too fast - so will give up on this for now - and go back to adding switches.
                                        I think I will add some switches directly on the extruder for the U/X Axis - to take advantage of the inputs available on the 1LC boards.
                                        Have applied the Io1.in Z probe change to both extruders now and tidyed up the wiring on the two extruders a fair bit.
                                        I think I need to get U & V end stops working properly - then 4 Z bed levelling working properly before I attempt my first print - as at present the rear axis seems to droop a bit - probably due to the 4 motors on it at the back.
                                        • o_lampeundefined
                                          o_lampe @dwuk3d
                                          "Goodby toolchanger" then? Isn't there a way to distribute the steppers to the left and right, keeping the front available for extra tools? Steppers aren't exactly lightweight and you'll need some beefy motors to overcome the friction of the idler pulley-orgy.
                                          I mentioned it before, but my hashPrinter only needed 4 motors for 4 semi-independent toolheads. The super simple gantry was the reason why I built it.
                                          • dwuk3dundefined
                                            dwuk3d @o_lampe
                                            @o_lampe Yes would be good if I could get down to 4 motors for 4 heads.
                                            May well explore other multi head options at some point - I guess the disadvantage of a hash printer is not easily being able to move heads not in use out of the way.
                                            I think it will be easier though in terms of belt paths to keep with the double Y axis approach - with belts just going between the front and back.
                                            Trying to keep to one extra motor per gantry would I think need the belts to run around both sides and either across the back or across the gantry.
                                            I'm not thinking of putting motors side by side at the front - just on top or below - so I don't think it will affect tool changing.
                                            On look at it a bit more closely I think on the bottom isn't going to work - so will just put one motor on the front top on each gantry - with the other two at the back.