    RC Low-Pass Filter for Blower Fan
    57
    9.3k
    • Iamturbo1978undefined
      Iamturbo1978 @wilriker
      @wilriker I'll try to make this as simple as I can, hopefully this will help.
      A PWM signal only has 2 states, "HIGH" and "LOW". for this example the voltage does not matter. It could be 12V, 5V, 3.3V etc... We don't care about the voltage right now, only the PWM signal.
      The PWM frequency is the number of PWM cycles in one second. If the frequency is 100Hz, then there are 100 PWM cycles in one second. Meaning, that each PWM cycle is only 0.01 seconds (10ms) long.
      The duty cycle is the ratio of how long the signal is high to how long it is low.
      If we have a duty cycle of 50%, the signal would be high for 0.005 seconds (5ms), then low for the remaining 0.005 seconds (5ms). If we set the duty for 30%, that would be 3ms high and 7ms low. and if we set it to 90%, that would be high for 9ms, and low for 1ms.
      The common way for a PWM cycle is to start high, wait the amount of time set by the duty cycle, then go low for the remaining amount of time. Not everything follows this way, but for this example, we are not going to worry about the other ways.
      Now, lets say our filter is tuned to only look at a single 10ms (100Hz) PWM cycle. It would only see the signal being high for sometime, then go low for sometime.
      But now lets change the filter to look at a 9ms (106Hz) PWM cycle. It would see the high like the last filter, but the low would be shorter than the other filter.
      Lets set the duet duty cycle to 50%, and the frequency to 100Hz (10ms cycle). The duet would make the signal high for 5ms, then low for 5ms. Now we add the 106Hz filter. The filter is only going to see 9ms of the PWM cycle. So that would be 5ms high, then 4ms low. That would mean the signal is high 80% of the time ((4ms/5ms)*100). That means, even though you set the duet to 50%, your fan would see 80%.
      Capacitors are like water towers. They store a charge, and depending on there size, they can store a little or a lot of charge. That stored charge takes time to discharge. Larger caps take more time to discharge, just like water towers. Everytime the PWM signal goes high, the cap gets charged. And every time the signal goes low, the cap gets discharged. How much discharged depends on the load, your fan for example. If the cap cant discharge most of the energy before the next PWM cycle, the cap gets recharged before it can discharge. If you keep putting in a 80% PWM duty cycle into a cap, but only using 40% of the energy, the cap would be fully charged in only 2 PWM cycles or 20ms. That is why your fan stays on no matter what duty cycle you set. And that is why the lower frequency helped, there was more time for the cap to discharge.
      The advice I gave you before was me trying to get what you had on hand to at least help you. Without some kind of feedback from the fan, and a circuit to monitor and adjust the PWM on the fly automatically, you are not going to be able to get a direct correlation between the speed you set, and the actual speed of the fan.
      What I did is with my old ramps board is is found a R-C combination that removed the PWM noise from the my fan using the smallest cap I could use. I used a 100uF cap, and a 10Ω resister on a fan that has a 0.25A rating. If my fan used less power, I would have used a smaller cap.
      Hope that helped.
      wilrikerundefined 1 Reply Last reply Reply Quote 1
      • wilrikerundefined
        wilriker @Iamturbo1978
        @iamturbo1978 First of all a big thanks for this very detailed explanation. 👍
        I knew parts of it but there was some very interesting news in it.
        Especially that the PWM high-low-cycles are always within a cycle that is defined by the frequency. Up until now I always thought that it would combine the latter type of cycles to continues high and low phases. But the way you describe it makes a lot more sense because otherwise you would loose a lot of fine-control at very low frequencies.
        Also finally I understand cut-off frequency of the RC-filter.
        With one open question though: you say if we have 10ms cycles and a 106Hz filter will only see 9ms of these cycles - what happens with the remaining 1ms? A friend of mine just proposed that it will "stretch" what it sees to match the "outer" cycle, i.e. it will create a 10ms cycle out of what it sees but using the proportions it sees in 9ms.
        I guess I finally have to buy a book on electronics. 😂
        Manuel
        My Tool Collection
        Iamturbo1978undefined 1 Reply Last reply Reply Quote 0
          There is a complication which makes the R-C filer much worse in this application. The output of a Fan connector is not a square wave with a variable mark-space ratio. It is a switch (the mosfet) that alternately connects the load to V_Fan and leaves it unconnected (save for the flyback diode on later Duets) with a variable mark-space ratio. The difference is that when the switch is off, the capacitor does not discharge through the resistor. It discharges only through the load. This means that the voltage at the output of the R-C filter will always be higher than the mark-space ratio implies, after allowing for the loss in the resistor. Whereas with an inductor (of a sufficient value for the PWM frequency being used) instead of the resistor the flyback diode completes the circuit when the switch is off, so you do get an output voltage that is proportional to the mark-space ratio.
            @wilriker I'm glad it helped you to understand whats going on.
            With your open question; the PWM cycle does not reset, so the remaining 1ms after the filter would be added to the next cycle.
            cycle 1)
            high for 5ms, low for 4ms
            cycle 2)
            low for 1ms, high for 5ms, low for 3ms
            cycle 3)
            low for 2ms, high for 5ms, low for 2ms
            I agree with @dc42, to get the best output is to use a L-C filter.
            • wilrikerundefined
              wilriker
              Thanks @dc42 and @Iamturbo1978 for all your patience with me so far and for your very understandable explanations in this topic! 👍
              Just to make sure I understood everything correct here is a drawing of what it should look like:
              Of course power-source, MOSFET and flyback diode are already on the board and I would have to add the right half of the diagram. Right?
              Manuel
              My Tool Collection
                Yes, that's correct.
                • wilrikerundefined
                  wilriker
                  @dc42 Yesterday I connected the tacho output of the fan to my Duet. Although this fan is obviously not a 4-wire PWM fan it gives me quite stable RPM readings when I set my fan to a specific speed.
                  You said it might be that still this would give me bogus values and I found something really strange so maybe you could tell me if that could fall under what you warned me about:
                  My fan according to its specs (TFD-B5015M12B) has a top speed of 4500 RPM@12V. If I run it with M106 S1 it will get full Vin which in my case is 13.6V so of course it will run faster. But tacho readings tell me it runs at 6500 RPM. If I then run it with M106 S0.88 it should get very close to 12V and the tacho reads 5500 RPM. Interestingly there is another model of the same family that would have exactly this speed @12V but I checked my order as well as the type label on my fan to not be the faster model.
                  Of course there is a chance that my fan is labelled wrong or that they have changed the specs since this specific fan was produced. But I just wonder would it be possible for the RPM reading to be off at around 1000 RPM and scale according to this?
                  Manuel
                  My Tool Collection
                  • JoergS5undefined
                    JoergS5 @wilriker
                    @wilriker so this could be the H type with 5500. If you measure the current also, and it is 0.18 A instead of 0.14, then you have the other type.
                    • wilrikerundefined
                      wilriker @JoergS5
                      @joergs5 To measure the current I would have to put my multimeter in series, right? Never done that so far.
                      Manuel
                      My Tool Collection
                      • JoergS5undefined
                        JoergS5 @wilriker
                        @wilriker directly into one of the main lines of the blower. Disconnecting the line and putting the current meter at those two open contacts. Be aware to set the maximum measure value of the current meter high first (above the maximum ampere, e. g. 1 A).
                        If it's a Molex connection, you can turn current off, draw out one of the cables (the pin have a barb, by pressing down you can remove the cable), connect to amperemeter at both sides, turn on and then measure.
                        • wilrikerundefined
                          wilriker @JoergS5
                          @joergs5 OK, thanks for confirming. As I already cut my wires to the fan I think I can quite easily insert the multimeter in this circuit using some screw terminals... I need to put ferrules on the wire ends anyway, so that's up next.
                          Then again it would be really strange to have the H type when buying the M type that is also labelled as being the M type (including the amperage). I would expect this on a super-cheapo Chinese fan but not from a brand. But let's wait and see. 😀
                          Manuel
                          My Tool Collection
                          • JoergS5undefined
                            JoergS5 @wilriker
                            @wilriker maybe labeled by someone who needs better glasses, M and H are similar 😉
                            I thought it may be the H type because your 5500 measuring fits exactly to this higher model.
                            • wilrikerundefined
                              wilriker @JoergS5
                              @joergs5 I know it would fit perfectly. Also about 6500 RPM @13.6V would match that quite well.
                              Manuel
                              My Tool Collection
                              • SnowCrashundefined
                                SnowCrash
                                @phaedrux said in RC Low-Pass Filter for Blower Fan:
                                https://www.digikey.ca/short/jrmcdf
                                I was reading through this thread and was hoping someone could clarify the value of the inductor in the diagram above? I'm familiar with 1uH (micro-Henry) and 1nH (nano-Henry), but what does 1mH stand for? mili-Henry (1000uH)? for such a small amount of current?
                                • wilrikerundefined
                                  wilriker @SnowCrash
                                  @snowcrash said in RC Low-Pass Filter for Blower Fan:
                                  Yes, mH is milli-Henry.
                                  Manuel
                                  My Tool Collection
                                  SnowCrashundefined 1 Reply Last reply Reply Quote 0
                                    SnowCrash @wilriker
                                    Thanks @wilriker!
                                    But that's HUGE just for a fan that draws maybe 0.15mA, no? (ok, the fan will draw more current at startup but still...). Is there some calculation behind this value?
                                    wilrikerundefined dc42undefined 2 Replies Last reply Reply Quote 0
                                    • wilrikerundefined
                                      wilriker @SnowCrash
                                      @snowcrash Actually I have no clue about all this stuff. I just took those numbers for granted (even though I would also like to learn about where they come from).
                                      But just as an update: I dropped all this anyway since connecting the signal line showed that the fan actually turns at the speed I set it to, it just feels/sounds a lot lower - but then my ears and fingers are probably the worst way of measuring fan speed in the first place. 😂
                                      Manuel
                                      My Tool Collection
                                        SnowCrash @wilriker
                                        @wilriker happy you got your fan working quietly (though perhaps not in the way you were hoping to achieve this 🙂 )
                                        Anyway, at another discussion, @dc42 insisted that an inductor-capacitor circuit is necessary for preventing a non-PWM fan from potentially being damaged while being run with a high frequency PWM signal, and just I started looking into the idea of making a little add-on module that would provide this circuitry for all 3 PWM outputs on the Duet (plus the ability to choose between 12V and 24V for each fan which is the main reason for the module).
                                        So hopefully @dc42 or someone else familiar with this subject would chime in and clarify this point about the inductor's value.
                                          dc42 administrators @SnowCrash
                                          Thanks @wilriker!
                                          Yes 1mH. The fan draws 0.15A (150mA), not 0.15mA.
                                            SnowCrash @dc42
                                            Thanks for the confirmation, @dc42! But what's the calculation behind it?