Tool board - no response
-
Can you send m98 p"config.g" and post the results?
Do you have your other tool boards connected as well?
-
@phaedrux
I don´t have the other connected, yet.Error: Response timeout: CAN addr 123, req type 6027, RID=96
Error: Fan number 5 not found
Error: in file macro line 82 column 13: M106: expected number after 'H'
11.8.2021, 22:44:22 Error: Response timeout: CAN addr 123, req type 6027, RID=94
Error: Fan number 4 not found
11.8.2021, 22:44:20 Error: Response timeout: CAN addr 122, req type 6027, RID=90
Error: Fan number 2 not found
Error: Response timeout: CAN addr 122, req type 6027, RID=92
Error: Fan number 3 not found
11.8.2021, 22:44:16 Error: Response timeout: CAN addr 123, req type 6026, RID=82
Error: Heater 3 not found
Error: Heater 3 does not exist
11.8.2021, 22:44:14 Error: Response timeout: CAN addr 122, req type 6043, RID=68
Response timeout: CAN addr 123, req type 6043, RID=69
Error: bad grid definition: X range too small
Error: Response timeout: CAN addr 122, req type 6031, RID=76
Error: Response timeout: CAN addr 122, req type 6026, RID=78
Error: Heater 2 not found
Error: Heater 2 does not exist
Error: Response timeout: CAN addr 123, req type 6031, RID=80
11.8.2021, 22:44:06 Error: Response timeout: CAN addr 122, req type 6042, RID=64
Response timeout: CAN addr 123, req type 6042, RID=65
11.8.2021, 22:44:04 Error: Response timeout: CAN addr 122, req type 6042, RID=60
Response timeout: CAN addr 123, req type 6042, RID=61
11.8.2021, 22:44:02 Error: Response timeout: CAN addr 122, req type 6042, RID=56
Response timeout: CAN addr 123, req type 6042, RID=57
11.8.2021, 22:44:00 Error: Response timeout: CAN addr 123, req type 6018, RID=53
Driver assignments: X1.1 Y0.0:0.1 Z0.2:0.3:0.4:0.5 E121.0:122.0:123.0, 3 axes visible
11.8.2021, 22:43:59 m98 p"config.g"
Error: Response timeout: CAN addr 122, req type 6018, RID=52 -
@barbarossa-cologne
Hot end fan is running.
Print cooling fan is not running.
I can´t control both. -
How is the PT1000 connected?
Is it actually a PT1000?Photos of your toolboard wiring?
-
@phaedrux
It's the original tool changer thermistor.
Is it a pt100?
Oh no... -
-
@barbarossa-cologne
-
@barbarossa-cologne I've seen that crazy temperature value once before when a tool board was configured for a PT1000 sensor but the sensor wasn't connected.
-
@dc42 that's what I checked another time 2 minutes ago. It's definitely connected.
-
@barbarossa-cologne have you measured its resistance, to verify that it is a PT1000, not a PT100 or a thermistor?
-
@dc42 connected a different thermistor = same problem
-
@dc42
Yes. Now I connected a typical Chinese thermistor and it shows the same number for temperature:/ -
@barbarossa-cologne the config.g file you posted was for a PT1000, not a thermistor. Specifically, this line:
M308 S1 P"121.temp0" Y"pt1000" R2200 ; configure sensor 1 as PT1000 on pin 121.temp0
-
@dc42
Eeeehm ok.
Yes
That was the problem...
SOLVED
thanks a lot