    Z tool pre-setter sensor wiring
    457
    • RockBundefined
      RockB
      I want to use a high-precision tool setter limit switch (https://www.automationdirect.com/adc/shopping/catalog/sensors_-z-_encoders/limit_switches/plunger_actuator/p11ddb-duld) as a Z probe in a multi-tool tool changer machine. Each tool will come down and touch this sensor as part of Z calibration.
      The sensor only has two wires and was wondering what would be the best way to wire this.
      Datasheet: https://cdn.automationdirect.com/static/specs/lshighprectoolsetls.pdf
      Since there is no "signal" input to wire into the IO port on Duet3 mainboard, What would be the best way to wire and configure this 2-wire sensor as a Z probe?
        jay_s_uk @RockB
        @RockB which one did you get? With or without the LED?
        RockBundefined 1 Reply Last reply Reply Quote 0
        • RockBundefined
          RockB @jay_s_uk
          @jay_s_uk One with LED. Both are two wires though. There is no separate "signal" wire that can be wired to iox.in; Hence was a little confused.
          • RockBundefined
            RockB @RockB
            @jay_s_uk @droftarts @dc42 any suggestions?
            There is an LED indicator on the sensor and a 10mA limit so the LED doesn't get damaged when connected to 24V. I have soldered a 2K ohm resistor to limit the current. Simple testing by directly connecting the brown wire to +24V and black to GND works fine. The sensor is NC, and pressing the plunger breaks the circuit.
            I was thinking of connecting the brown (+) to iox.in and black (-) to the GND in the IO port of Duet3 6HC and enabling pull-up resistor. Still need to connect it to 24V to power it and I am not sure how to do this with only two wires.
            jay_s_ukundefined dc42undefined 2 Replies Last reply Reply Quote 0
              jay_s_uk @RockB
              @RockB ioX.in and ground would be the usual way and that would be the way to connect the without LED version. Not sure for the one you've got though
                dc42 administrators @RockB
                @RockB here's one option. Connect the switch plus 2K series resistor between +24V and the IO_IN pin of your selected port. Connect a resistor of about 330 ohms between the IO_IN pin and ground.
                RockBundefined 1 Reply Last reply Reply Quote 1
                • RockBundefined
                  RockB @dc42
                  @dc42 Thanks for the info. I have created a circuit as below. The brown and blue wires represent the two wires from the switch/sensor.
                  I have tested the voltage between io3.in and GND using a multimeter. When the Switch is not pressed, the reading is about 1.8V, and when the switch is pressed, the reading changes to 19.8V
                  I have configured a Z probe in config.g as follows:
                  ; Z Probe
                  M558 K0 P5 C"!io3.in" ; Z-probe tool setter connected to io3.in pin
                  However, when the value of the Z probe in DWC doesn't seem to change. It just stays at 0. Even manually pressing the switch to trigger it does nothing, but I can see the voltages change in the multimeter
                  Any suggestions as to why the Z probe value in DWC is not changing?
                  I plan to use M585 to determine Z height during probing.
                    Phaedrux Moderator @RockB
                    @RockB said in Z tool pre-setter sensor wiring:
                    K0
                    since you've defined K0 you must include a K0 in all other references to the probe usage and configuration. Eg G30 K0
                    If you only have a single Z probe, just leave the K0 off entirely.
                    • RockBundefined
                      RockB @Phaedrux
                      @Phaedrux Understood, but the issue seems to be the Z probe not changing value in DWC even with manual triggering. The documentation says to expect 0 when not triggered and 1000 when triggered.
                      Checking the voltages using a multi-meter, I can clearly see the change from 1.9V to 19.8V with manually pressing the Z probe/switch.
                      Any suggestions on what is going on and why the Z probe value is not changing?
                      • oliofundefined
                        oliof @RockB
                        @RockB it's possible the probe triggers and the print head lifts fast enough after triggering that DWC doesn't update the display
                        • RockBundefined
                          RockB @oliof
                          @oliof Thank you for the suggestion but there is no print head movement in this test. I am pressing the switch manually and actually holding it pressed for a few seconds. Still no change in Z probe reading shown in DWC and also in Object model.
                            Firmware and DWC version?
                            • RockBundefined
                              RockB @Phaedrux
                              @Phaedrux FW and DWC both at 3.5.2
                                droftarts administrators @RockB
                                @RockB io3.in expects between 0V and 3.3V to trigger it, but has a threshold somewhere between (probably around 1.5 or 1.6V) between being not triggered and triggered. If you're getting between 1.9V and 24V, io3.in will be permanently triggered. The ! in the pin definition inverts this, so it is permanently NOT triggered. Did you add the 330 ohm resistor between io3.in and GND, as @dc42 suggested? This should pull down the 1.8V to 0V.
                                Does the LED light up on the switch?
                                • RockBundefined
                                  RockB @droftarts
                                  @droftarts Ian, I tried adding the 330 ohm resistor between io3.in and GND - this causes the original 19.8V to drop to 3.2 V when switch is pressed (open); however in its closed (default) condition the voltage just drops from 1.9V to 1.8V. So now I am getting voltages in the range 1.8V to 3.2V and the lower voltage is still higher than the threshold for input pin.
                                  LED does light up on the switch when powered (default state is NC) and goes off when pressed (open) as it should.
                                  Any suggestions on how to further reduce the lower voltage so that it’s below the threshold? A circuit diagram would be helpful.
                                    @RockB I think you misunderstood @dc42's suggestion. It should be 24V > Switch > 2.2k resistor > io3.in > 330 ohm resistor > GND, ie a voltage divider circuit. Something like this:
                                    The wire between the resistors connects to io3.in. Here's a circuit simulation: https://tinyurl.com/233sf6pk
                                    With the switch closed, io3.in gets 3.3V. When it's open, it's not connected, so should be 0V.
                                    RockBundefined 2 Replies Last reply Reply Quote 0
                                    • RockBundefined
                                      RockB @droftarts
                                      @droftarts Ah! This makes sense. Will give this a try. Thanks
                                      • RockBundefined
                                        RockB @droftarts
                                        @droftarts Tested this and works as expected. Just changed the 2K resistor to a 2.7K resistor to limit the overall current below 10mA. Thanks
