    RRF3 -> Z-Probe was not triggered during probing move
    38
    2.6k
    • JoergS5undefined
      JoergS5 @CR3D
      @CR3D could be that the Duet 2 and Duet 3 have different pullup default values and your probe makes a different. If ^ does not work, I am sure a solution to add some external pullup resistor to the endstop would be also possible to set the same resitance comparable to the Duet 2 was.
      I visited your homepage, you have interesting and good quality printers!
      A Former User? CR3Dundefined 2 Replies Last reply Reply Quote 0
        A Former User @JoergS5
        @JoergS5 said in RRF3 -> Z-Probe was not triggered during probing move:
        1k vs 27k hardware pull up
        • CR3Dundefined
          CR3D @JoergS5
          @JoergS5
          Thank you! Yes we want to build high performance Printers with High performance Electronics! 😉
          @bearer
          Thank you -> is that difference a problem for the sensor or the result? because the sensor at itself triggers ...
          the question is still why he moves the z-axis too far after probing ..?
          Christian from CR-3D
          Homepage:
          www.cr-3d.de
          Facebook:
          https://www.facebook.com/cr3d.official
          Our Discord Server
          https://discord.gg/SxRaPNuRdA
          Thingiverse Profile:
          https://www.thingiverse.com/cr-3d_official/about
          • CR3Dundefined
            CR3D
            Ok i made every changes you said and nothing was the solution!
            M558 P5 C"^!io5.in" H1 F500 T12000 ; Z probe type -> Induktiv
            G31 P100 X0.0 Y0.0 Z1.95
            I activated the Pull-Up Resistor and i changed again the DIVE Heigth ("H-Parameter").
            it must be a bug in the firmware, it only moves the bed with the G29 by twice the dive height without knowing this. Then, of course, the distance to the Z-Probe is too great and it gives the error message "Z-Probe was not triggered during probing move"
            the inductive sensor itself works wonderfully -> I also use it on the X, Y and U axis. So it is not a problem with the signal evaluation in my opinion!
            Homepage:
            www.cr-3d.de
            Facebook:
            Our Discord Server
            • CR3Dundefined
              CR3D
              @dc42 do you have any idea? Please help me...!
              Homepage:
              www.cr-3d.de
              Facebook:
              Our Discord Server
              • JoergS5undefined
                JoergS5 @CR3D
                @CR3D if you start G29, is the first mesh testing point over the bed? The first point is at 50,0 and your offset setting is 0,0 which is strange (same position like nozzle?) But mesh ignores G31 setting anyway and starts at 0,50. I would try starting eg at 100,100
                Other ideas are whether Ir is reflected correctly by print bed.
                Third idea is the prebuilt pullups may be too weak. The Duet Ir Sensor mentions the smoothieboard 1k pullups being too weak eg. Maybe this hereis a similar problem. But I am no pullup expert.
                Article with section smoothieware: https://miscsolutions.wordpress.com/mini-height-sensor-board/
                One more idea, I miss the M574 Z endstop saying that the z endstop is a probe:
                "When using the Z probe to home Z, M574 Z0 should be used."
                One additional idea is that LEDs are mentioned in the config, maybe the light disturbs the IR sensor. Maybe they emit IR wavelengths partly.
                CR3Dundefined 1 Reply Last reply Reply Quote 0
                • CR3Dundefined
                  CR3D @JoergS5
                  Thank you for the many suggestions, but unfortunately all the points mentioned are given.
                  The first rehearsal point is over the bed! That fits.
                  the funny thing is that he sometimes brings the error message right after the first probe point and sometimes right in the middle or once it had worked completely to execute the G29 command, but then the complete heightmap had an offset of 5mm (see image above).
                  And by the way I use an inductive sensor and no longer the IR probe -> I've had too many problems with this in the past ...
                  Homepage:
                  www.cr-3d.de
                  Facebook:
                  Our Discord Server
                    deckingman @CR3D
                    @CR3D This is a long shot because I don't use a probe, but try reducing the feed rate in your M558. e.g. try 300 instead of 500 just to see if that helps.
                    • MacNiteundefined
                      MacNite
                      If looked through your code and could not find any mistakes. I had some Problems in my beginngs with RRF3 too.
                      Maybe @dc42 has another Idea.
                      Greets
                      Max
                      CorEssentials on GitHub | Instructables Profile | Thingiverse Profile
                        Just to eliminate the probe entirely can you test using M558 P0 to use the manual probing option? That will prompt you to job the Z axis down. Then we can see if everything software side is working with the homing heightmap etc.
                        Maybe the probe itself is failing. Do you have another to test with?
                        • CR3Dundefined
                          CR3D @Phaedrux
                          I have already exchanged the z-probe a few times. I have already made 20 repetitions with the homez.g and measured the trigger height, so the sensor triggers wonderfully and works very precisely (approx. 0.01mm).
                          It only occurs with the G29 command.
                          Again I have observed that with G29 it not only moves the dive height down, but the double dive height. In the dashboard, however, the "simple" dive height is shown as the Z value. that's why i think it moves twice its height and doesn't notice it.
                          as soon as he then carries out a test point in the G29, he has to cover twice without knowing that he drove this height before, so he claims that the z-probe does not trigger.
                          Another dive height does not change anything, because it then moves twice without knowing it. 😞
                          Homepage:
                          www.cr-3d.de
                          Facebook:
                          Our Discord Server
                          • Skimmyundefined
                            Skimmy
                            I did an extensive code-check and talk with CR3D and also didn't come to a solution.
                            For example: a 5-point bed-calibration works fine (a G32 (call to execute bed.g with 5x G30 in it)
                            Every G30 command works, but as soon as you start a G29, things start getting weird.
                            my blog: https://www.well-engineered.net
                              In your config.g file I see these lines:
                              M584 X0.2 Y0.0:0.1 U0.3 Z1.0:1.1:1.2 E0.4:0.5 ; set drive mapping
                              and:
                              M558 P5 I1 C"!io5.in" H5 F500 T12000 ; Z probe type -> Induktiv
                              So your Z motors are connected to the expansion board and your Z probe is connected to the main board. Unfortunately, it is a limitation of the current firmware that an endstop switch or Z probe connected to the main board cannot stop a stepper motor connected to an expansion board unless a motor connected to the main board is also moving. This was documented for endstops some time ago (at https://duet3d.dozuki.com/Wiki/Duet_3_firmware_configuration_limitations and also in the RRF 3.0 release notes at https://github.com/Duet3D/RepRapFirmware/blob/v3-dev/WHATS_NEW_RRF3.md), but unfortunately I omitted to include Z probes in those documents until recently. I apologise for that.
                              Possible workarounds include:
                              1. Connect the three Z motors to stepper outputs on the main board. This is the preferred solution.
                              2. Connect the inductive sensor to the expansion board instead of to the main board.
                              3. Configure a 4th dummy Z motor on the main board.
                                T3P3Tony administrators
                                looking at your motor use, it looks like you are using all the drivers on the mainboard so I think you need to swap Z to the main board or the sensor to the expansion board.
                                • Karmaundefined
                                  Karma @CR3D
                                  @CR3D I was looking at your config.g file and I noticed that you have your Y-axis current set to 4200. I am not second guessing you, I was just wondering if that was correct.
                                  • CR3Dundefined
                                    CR3D @dc42
                                    Thank you david for your answer, that appears after a correct solution. But only as a counter question, why does a "single probe with G30" work very reliably with the Z probe on the mainboard and the motors on the expansion board?
                                    I did repeat tests and had results of about 0.01mm with single probing ...
                                    but no matter ... it makes sense to connect both on the same board!
                                    Yes I know this limitation... I swapped the Z-motors to the expansion board, because some days ago we had following problem, and there was no other solution to swap the Y-motors to the main board.
                                    https://forum.duet3d.com/topic/17153/duet3-expansion-board-3hc-no-can-connection/50?_=1594149269971
                                    With this problem at the time, I even had the endstops on the 3HC board and it still didn't work.
                                    That is why the three Z-axes are now on the expansion board. This made me forget to put the Z-probe from the main board onto the expansion board.
                                    I just tried to test it, hoping to find the solution here. I put the Z-probe on the PIN C "^! 1.io5.in".
                                    M558 K0 P5 C"^!1.io5.in" H5 F400 T10000 ; Z probe type -> Induktiv
                                    As soon as I plug in the z-probe here and adjust the config, the Z-probe disappears from the dashboard and with a probe command the error message appears that the Z-probe could not be found.
                                    As soon as I plug it back into the main board, it appears again!
                                    what can be the problem here?
                                    Plugging the Z motors onto the mainboard is not an option due to the homing error mentioned above for the Y axis.
                                    Or would it be possible to have one motor (i.e. 1x Y and 1x Z) on the main board and the others on the expansion board?
                                    @Skimmy special thanks for the detailed examination of the code the last days 🙂
                                    @Karma : I use NEMA 23 motors at the y-axis and they need this current
                                    many thanks for the numerous answers! I hope, we find a solution 🙂
                                    Regards Christian (CR-3D)
                                    Homepage:
                                    www.cr-3d.de
                                    Facebook:
                                    Our Discord Server
                                    Karmaundefined dc42undefined 2 Replies Last reply Reply Quote 1
                                    • Karmaundefined
                                      Karma @CR3D
                                      @CR3D Ahh, that makes perfect sense now. Thank you for that answer.
                                      I would live to get my hands on a Duet 3, but my wife would kick my rear end if I spent anymore money on my printer right now. The Duet 3 board has so many more options then any board I have every seen. It's truly a work of art.
                                      • CR3Dundefined
                                        CR3D
                                        I even tested it now to always place at least one motor on the respective axis (i.e. a motor with the 3 z-axes on the mainboard and one of the two Y-axes on the expansion board) and map it correctly in the config. But this didn't work at all, not all axles drive clean here!
                                        Why doesn't the Z-Probe work on the expansion board? That would be the easiest way ...?
                                        Homepage:
                                        www.cr-3d.de
                                        Facebook:
                                        Our Discord Server
                                          dc42 administrators @CR3D
                                          @CR3D said in RRF3 -> Z-Probe was not triggered during probing move:
                                          One of the listed limitations is that a Z probe connected to an expansion board must be type 8 or type 9. So change the P parameter in your M558 command from P5 to P8.
                                          • CR3Dundefined
                                            CR3D @dc42
                                            Thank you... also my mistake... sorry
                                            But now to my test result:
                                            As usual, I connected all Z-motors to the expansion board and also the Z-probe to the expansion board.
                                            See config:
                                            G90            ; send absolute coordinates...
                                            M82            ; and absolute extruder moves
                                            M550 P"I444-S" ; set printer name
                                            M552 S1        ; enable network
                                            M586 P0 S1     ; enable HTTP
                                            M586 P1 S0     ; disable FTP
                                            M586 P2 S0     ; disable Telnet
                                            M569 P0.0 S1   ; physical drive 0.0 goes forwards Y0
                                            M569 P0.1 S0   ; physical drive 0.1 goes forwards Y1
                                            M569 P0.2 S0   ; physical drive 0.2 goes forwards X
                                            M569 P0.3 S0   ; physical drive 0.3 goes forwards X1 (U)
                                            M569 P0.4 S0   ; physical drive 0.4 goes backwards E0
                                            M569 P0.5 S0   ; physical drive 0.5 goes backwards E1
                                            M569 P1.0 S1   ; physical drive 1.0 goes forwards Z0
                                            M569 P1.1 S1   ; physical drive 1.0 goes backwards Z1
                                            M569 P1.2 S1   ; physical drive 1.0 goes forwards Z2
                                            ;New Mapping
                                            M350 X16 Y16 U16 Z16 E16:16 I1  ; configure microstepping
                                            M92 X80.00 Y35.56 U80 Z1600 E415:415 ;set steps per mm
                                            M566 X300 Y300 U300 Z12 E300:300   ;set maximum instantaneous speed changes (mm/min)
                                            M203 X60000 Y60000 U60000 Z1000 E9000:9000      ;set maximum speeds (mm/min)
                                            M201 X1000 Y1000 U1000 Z200 E1000:1000            ;set accelerations (mm/s^2)
                                            M906 X1400 Y4200 U1200 Z1500 E1000:1000 I30  ;set motor currents (mA)
                                            M84 S30             		    ; Set idle timeout
                                            M208 X0 Y0 U91 Z0 S1     ; set axis minima
                                            M208 X460 Y500 U551 Z420 S0         ; set axis maxima
                                            M574 X1 S1 P"!io1.in" ; active-high endstop for low end on X via pin io0.in
                                            M574 U2 S1 P"!io0.in" ; active-high endstop for high end on U via pin 1.io1.in
                                            M574 Y2 S1 P"!io2.in" ; active-high endstop for high end on Y via pin 1.io2.in
                                            M574 Z1 S2
                                            M558 K0 P8 C"^!1.io5.in" H5 F400 T10000 ; Z probe type -> Induktiv
                                            ;Z-Probe Piezo
                                            ;M558 P5 C"!io3.in" R1.0 K0 H5 F200 T6000 ; Z probe type -> Piezo
                                            ;M558 P5 C"!io4.in" R1.0 K1 H5 F200 T6000 ; Z probe type -> Piezo
                                            ;G31 K0 P100 X0.0 Y0.0 Z-0.30
                                            ;G31 K1 P100 X0.0 Y0.0 Z-0.30
                                            M557 X80:330 Y30:310 P04:04      ; define mesh grid
                                            M308 S0 P"temp0" Y"thermistor" T100000 B4092          ; configure sensor 0 as thermistor on pin temp0
                                            M950 H0 C"out0" T0                                    ; create bed heater output on out0 and map it to sensor 0
                                            M307 H0 B0 S1.00                                      ; disable bang-bang mode for the bed heater and set PWM limit
                                            M140 H0                                               ; map heated bed to heater 0
                                            M143 H0 S120                                          ; set temperature limit for heater 0 to 120C
                                            M308 S1 P"temp1" Y"thermistor" T100000 B4725 C7.06e-8 ; configure sensor 1 as thermistor on pin temp1
                                            M950 H1 C"out1" T1                                    ; create nozzle heater output on out1 and map it to sensor 1
                                            M307 H1 B0 S1.00                                      ; disable bang-bang mode for heater  and set PWM limit
                                            M308 S2 P"temp2" Y"thermistor" T100000 B4725 C7.06e-8 ; configure sensor 2 as thermistor on pin temp2
                                            M950 H2 C"out2" T2                                    ; create nozzle heater output on out2 and map it to sensor 2
                                            M307 H2 B0 S1.00                                      ; disable bang-bang mode for heater  and set PWM limit
                                            M950 F0 C"out4"                                   ; create fan 2 on pin out4 and set its frequency
                                            M106 P0 S0 H-1                                        ; set fan 2 value. Thermostatic control is turned off
                                            M950 F1 C"out5"                                  ; create fan 3 on pin out5 and set its frequency
                                            M106 P1 S1 H2:1 T50                                   ; set fan 3 value. Thermostatic control is turned off
                                            M563 P0 S"Links" D0 H1 F0  ; define tool 0
                                            G10 P0 X0 Y0 Z0 S0 R0        ; set tool 0 axis offsets
                                            M563 P1 S"Rechts" D1 H2 X3 F0   ; define tool 1
                                            G10 P1 Y0 U0 Z0 S0 R0        ; set tool 1 axis offsets
                                            ; Custom Safety Settings
                                            ; Open Door Switch
                                            M950 J0 C"!1.io0.in"
                                            M950 J1 C"!1.io1.in"
                                            M950 J2 C"!1.io2.in"
                                            ; Emergency Stop
                                            M950 J3 C"!1.io3.in"
                                            M581 T0 C"1.io3.in"  S0 C0		;trigger #2 (calls trigger0 -> Emergency-Stop)
                                            M582 T0
                                            ; LEDs
                                            ; Farbe Blue
                                            M950 F2 C"out3" Q500  ; create fan 3 on pin out5 and set its frequency
                                            M106 P2 S119     ;set fan 3 value. Thermostatic control is turned off
                                            ; Farbe Red
                                            M950 F3 C"1.out0" Q500  ; create fan 3 on pin out5 and set its frequency
                                            M106 P3 S0     ;set fan 3 value. Thermostatic control is turned off
                                            ; Farbe Green
                                            M950 F4 C"1.out1" Q500  ; create fan 3 on pin out5 and set its frequency
                                            M106 P4 S117     ;set fan 3 value. Thermostatic control is turned off
                                            ; Farbe White
                                            M950 F5 C"1.out2" Q500  ; create fan 3 on pin out5 and set its frequency
                                            M106 P5 S0     ;set fan 3 value. Thermostatic control is turned off
                                            M501          ; load saved parameters from non-volatile memory
                                            T0            ; select first tool
                                            M400
                                            M572 D0 S0.03
                                            My config-override:
                                            ; config-override.g file generated in response to M500 at 2020-07-06 20:53
                                            ; Heater model parameters
                                            M307 H0 A53.3 C44.6 D1.1 S1.00 V23.9 B0
                                            M307 H1 A967.6 C371.4 D5.4 S1.00 V23.7 B0
                                            M307 H2 A340.0 C140.0 D5.5 S1.00 V0.0 B0
                                            ; Probed tool offsets
                                            G10 P0 X0.00 Y0.00 Z0.00 U0.00
                                            G10 P1 X0.00 Y0.00 Z-0.13 U0.00
                                            G31 K0 P500 X40.0 Y30.0 Z1.40
                                            ; Workplace coordinates
                                            G10 L2 P1 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P2 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P3 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P4 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P5 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P6 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P7 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P8 X0.00 Y0.00 Z0.00 U0.00
                                            G10 L2 P9 X0.00 Y0.00 Z0.00 U0.00
                                            now i have carried out another test.
                                            First home home all axes and then G29.
                                            And here unfortunately the same result again! The first probe point at the corner was fine... the second one causes following error 😞
                                            As already described above, this can only happen after several probe points!
                                            please note as always the probe is triggered even though it causes the error!
                                            So that was not the solution to the problem ... are there any other solutions?
                                            Homepage:
                                            www.cr-3d.de
                                            Facebook:
                                            Our Discord Server