    • fcwiltundefined
      fcwilt @KevinMar
      last edited by

      @kevinmar said in Tool Board Heater Tuning Leading To Faults:

      @fcwilt 206b714d-0f6e-4af1-b468-c804880c2ed3-image.png

      OK that helps.

      All all three heaters actually active at the same time?

      Do they all fault at the same time?

      Can you take a screen shot of the temp graph showing the heaters as they heat up and then fault?

      Frederick

      Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

      1 Reply Last reply Reply Quote 0
      • DIY-O-Sphereundefined
        DIY-O-Sphere @KevinMar
        last edited by

        @kevinmar
        Your sensor settings a looking wrong...

        Here is an example of mine
        M308 S1 P"temp1" Y"pt1000" R2200 ; configure sensor 1 as PT1000 on pin temp1

        (UTC+1)

        KevinMarundefined 1 Reply Last reply Reply Quote 1
        • fcwiltundefined
          fcwilt @KevinMar
          last edited by

          @kevinmar

          Please get in the habit of copy-and-pasting your files using the </> tag.

          M550 P"ToolChanger" 					; Set machine name
          M111 S0                              	; Debug off
          M929 P"eventlog.txt" S1					; Start logging to file eventlog.txt
          M555 P1									; Set RepRap output
          G21										; Set dimensions to millimetres
          G90										; Send absolute coordinates...
          M83										; ...but relative extruder moves
          M669 K1									; CoreXY mode
          G4 S1  									; Wait for expansion boards to start
          
          M569 P0.0 S1 D2							; Drive 0 direction | X
          M569 P0.1 S1 D2							; Drive 1 direction | Y
          M569 P0.2 S1 D2							; Drive 2 direction | Z
          M569 P0.4 S0 D2							; Drive 3 direction | C 
          M569 P0.5 S0 D2							; Drive 5 direction | A
          M569 P20.0 S0 D2						; Drive 6 direction | T0
          M569 P21.0 S0 D2						; Drive 7 direction | T1
          M569 P22.0 S0 D2						; Drive 8 direction | T2
          M569 P23.0 S0 D2						; Drive 9 direction | T3
          
          M584 X0 Y1 Z2 E20.0:21.0:22.0:23.0 C4 A5					; Axis to driver mapping 
          
          ; Set axis software limits and min/max switch-triggering positions.
          M208 X-35:320 Y-49:240 Z0:300 C-45:360 A0:55
          
          M350 X16 Y16 Z16 E16:16:16:16 A16 I1						; Configure microstepping with interpolation
          M350 C16 I10												; Configure microstepping without interpolation
          
          M906 X1800 Y1800 Z1000 I30									; Set motor currents (mA) and idle percent
          M906 E1500:1500:1500:1500 C500  I10							; Set motor currents (mA) and idle percent A400
          M203 X36000 Y36000 Z1200 C5000 E6000:6000:6000:6000 A6000	;Max speeds (mm/min)
          M201 X6000 Y6000 Z400 C600 E6000:6000:6000:6000 A1200		; Max Accelerations (mm/s^2)
          M566 X400 Y400 Z60 C6 E60:60:60:60 A360						; Max jerk (mm/min)
          
          M92 X100 Y100 Z800 E386:386:386:386 C91.022 A360			; Steps/mm 
          
          M574 X1 Y1 S3									; X / Y Endstop
          M574 Z1 S1 P"nil"								; Z Endstop 
          M574 C0											; Z / C No Endstop 
          
          M558 P5 C"!io0.in" H5 A5 T6000 S0.01 K0
          
          G31 P200 X0 Y0 Z0
          M557 X10:290 Y20:180 S40						; Define mesh grid
          
          M915 X Y S3 F0 H400 R2							; X / Y Axes
          M915 A S5 F0 H200 R2							; A Stall Detection
          
          ; Temperature sensors 
          M308 S0 P"0.temp0" Y"thermistor" T100000 B4138 C0 A"Bed" 
          M308 S1 P"20.temp0" Y"thermistor" T100000 B4725 C7.06e-8 A"Ex0"  
          M308 S2 P"21.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex1"  
          M308 S3 P"22.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex2"  
          M308 S4 P"23.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex3"  
          
          ; Heaters
          M950 H0 C"0.out1" T0						; Bed
          M140 H0										; Bed
          M950 H1 C"20.out0" T1						; Heater for extruder out tool 0
          M950 H2 C"21.out0" T2						; Heater for extruder out tool 1
          M950 H3 C"22.out0" T3						; Heater for extruder out tool 2
          M950 H4 C"23.out0" T4						; Heater for extruder out tool 3
          
          ; Heater PID Tuning
          M307 H0 R1.641 C353.300:353.300 D2.50 S1.00 V24.0 B0
          M307 H1 R1.590 C336.700:89.600 D5.00 S1.00 V23.8 B0
          M307 H2 R2.135 C314.200:86.000 D6.20 S1.00 V24.3 B0
          M307 H3 R2.023 C364.200:86.200 D5.70 S1.00 V23.7 B0
          M307 H4 R1.900 C383.000:383.000 D7.50 S1.00 V23.8 B0
          
          ;M307 H1 A849.7 C225.4 D5.9 S1.00 V24.2 B0  ; From Railcore with similar setup running V2.xx
          
          
          ; Max Temps
          M143 H0 S225
          M143 H1 S300
          M143 H2 S300
          M143 H3 S300
          M143 H4 S300
          
          ; Fans for hot end cooling
          M950 F10 C"20.out2"
          M106 P10 S255 H1 T70
          M950 F11 C"21.out2"
          M106 P11 S255 H2 T70
          M950 F12 C"22.out2"
          M106 P12 S255 H3 T70
          M950 F13 C"23.out2"
          M106 P13 S255 H4 T70
          
          ; Fans for part cooling
          M950 F0 C"20.out1"
          M950 F1 C"21.out1"
          M950 F2 C"22.out1"
          M950 F3 C"23.out1"
          
          
          M950 F7 C"^0.out9" Q600					;Wipe Servo
          M106 P7 C"Wipe" 						;Wipe Servo
          
          M302 S185 R185
          M404 N1.75 D0.4
          
          ; Tool definitions
          M563 P0 S"Tool0" D0 H1 F0
          G10  P0 S220 R205
          M563 P1 S"Tool1" D1 H2 F1
          G10  P1 S220 R205
          M563 P2 S"Tool2" D2 H3 F2
          G10  P2 S220 R205
          M563 P3 S"Tool3" D3 H4 F3
          G10  P3 S220 R205
          
          G29 S2
          M98  P"/sys/Toffsets.g"					; Set tool offsets from the bed
          T-1
          
          M501									; Load config-override.g
          

          Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

          DIY-O-Sphereundefined 1 Reply Last reply Reply Quote 1
          • KevinMarundefined
            KevinMar @DIY-O-Sphere
            last edited by

            @diy-o-sphere Huh, yeah that ain't right

            fcwiltundefined 1 Reply Last reply Reply Quote 1
            • dc42undefined
              dc42 administrators @KevinMar
              last edited by dc42

              @kevinmar if you are running without a silicone sock on the heater block, please add a silicone sock and re-tune. Your M307 parameters suggest that the fan substantially cools the hot end, which typically means that the fan is blowing on the heater block.

              Also please confirm that the part cooling fan is off when you command heating and the heater faults

              If after re-tuning with the silicone sock on (if necessary) the heaters still fault, you can try reducing the M307 R parameter. Try a 30% reduction.

              Duet WiFi hardware designer and firmware engineer
              Please do not ask me for Duet support via PM or email, use the forum
              http://www.escher3d.com, https://miscsolutions.wordpress.com

              KevinMarundefined 1 Reply Last reply Reply Quote 1
              • Dougal1957undefined
                Dougal1957
                last edited by

                M308 S2 P"21.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex1"
                M308 S3 P"22.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex2"
                M308 S4 P"23.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex3"

                Not sure if these lines are wrong or not for one you have the T B C and A params not sure if they are needed or correct for a PT1000

                fcwiltundefined 1 Reply Last reply Reply Quote 1
                • fcwiltundefined
                  fcwilt @KevinMar
                  last edited by

                  @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                  @diy-o-sphere Huh, yeah that ain't right

                  You are loading config-override.g at the end of config.g

                  Please post that file.

                  Frederick

                  Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

                  KevinMarundefined 1 Reply Last reply Reply Quote 0
                  • fcwiltundefined
                    fcwilt @Dougal1957
                    last edited by

                    @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                    M308 S2 P"21.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex1"
                    M308 S3 P"22.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex2"
                    M308 S4 P"23.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex3"

                    Not sure if these lines are wrong or not for one you have the T B C and A params not sure if they are needed or correct for a PT1000

                    From the docs:

                    Additional parameters for PT1000 sensors

                    Rnnn Series resistor value. Leave blank to use the default for your board.
                    Lnnn ADC low offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)
                    Hnnn ADC high offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)

                    Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

                    Dougal1957undefined KevinMarundefined 2 Replies Last reply Reply Quote 0
                    • Dougal1957undefined
                      Dougal1957 @fcwilt
                      last edited by

                      @fcwilt said in Tool Board Heater Tuning Leading To Faults:

                      @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                      M308 S2 P"21.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex1"
                      M308 S3 P"22.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex2"
                      M308 S4 P"23.temp0" Y"pt1000" T100000 B4725 C7.06e-8 A"Ex3"

                      Not sure if these lines are wrong or not for one you have the T B C and A params not sure if they are needed or correct for a PT1000

                      From the docs:

                      Additional parameters for PT1000 sensors

                      Rnnn Series resistor value. Leave blank to use the default for your board.
                      Lnnn ADC low offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)
                      Hnnn ADC high offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)

                      yes but the T100000 is for a ntc100k thermistor should not be required for a pt1000 nor a beta value as they are linear and don't have a c param either so not sure if having those params are confusing the issue

                      fcwiltundefined 1 Reply Last reply Reply Quote 0
                      • KevinMarundefined
                        KevinMar @fcwilt
                        last edited by

                        @fcwilt s

                        Rnnn Series resistor value. Leave blank to use the default for your board.
                        Lnnn ADC low offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)
                        Hnnn ADC high offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)

                        So Lnnn can offset the higher ambient reading?

                        fcwiltundefined 1 Reply Last reply Reply Quote 0
                        • KevinMarundefined
                          KevinMar @fcwilt
                          last edited by

                          @fcwilt I'm currently re-running the autotuning with the removed T, B, and C values from the config

                          Dougal1957undefined DIY-O-Sphereundefined 2 Replies Last reply Reply Quote 1
                          • Dougal1957undefined
                            Dougal1957 @KevinMar
                            last edited by

                            @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                            @fcwilt I'm currently re-running the autotuning with the removed T, B, and C values from the config

                            Good luck Kevin

                            Doug

                            KevinMarundefined 1 Reply Last reply Reply Quote 0
                            • DIY-O-Sphereundefined
                              DIY-O-Sphere @KevinMar
                              last edited by

                              @kevinmar
                              Put in the R value

                              (UTC+1)

                              Dougal1957undefined 1 Reply Last reply Reply Quote 0
                              • fcwiltundefined
                                fcwilt @Dougal1957
                                last edited by

                                @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                                yes but the T100000 is for a ntc100k thermistor should not be required for a pt1000 nor a beta value as they are linear and don't have a c param either so not sure if having those params are confusing the issue

                                I was trying to point out that R, L and N are the only additional parameters for PT1000 devices.

                                The B,C and T are clearly incorrect but are the affecting the heater or are they ignored since they don't apply?

                                I don't know.

                                Frederick

                                Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

                                Dougal1957undefined 1 Reply Last reply Reply Quote 0
                                • Dougal1957undefined
                                  Dougal1957 @DIY-O-Sphere
                                  last edited by

                                  @diy-o-sphere said in Tool Board Heater Tuning Leading To Faults:

                                  @kevinmar
                                  Put in the R value

                                  doesn't need it as it will default correctly

                                  1 Reply Last reply Reply Quote 0
                                  • Dougal1957undefined
                                    Dougal1957 @fcwilt
                                    last edited by

                                    @fcwilt said in Tool Board Heater Tuning Leading To Faults:

                                    @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                                    yes but the T100000 is for a ntc100k thermistor should not be required for a pt1000 nor a beta value as they are linear and don't have a c param either so not sure if having those params are confusing the issue

                                    I was trying to point out that R, L and N are the only additional parameters for PT1000 devices.

                                    The B,C and T are clearly incorrect but are the affecting the heater or are they ignored since they don't apply?

                                    I don't know.

                                    Frederick

                                    I agree neither do I know but it has to be worth a try

                                    1 Reply Last reply Reply Quote 1
                                    • fcwiltundefined
                                      fcwilt @KevinMar
                                      last edited by

                                      @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                                      @fcwilt s

                                      Rnnn Series resistor value. Leave blank to use the default for your board.
                                      Lnnn ADC low offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)
                                      Hnnn ADC high offset correction, default 0 (ignored if the hardware supports automatic ADC gain and offset calibration)

                                      So Lnnn can offset the higher ambient reading?

                                      I have no idea. Never used PT1000 devices.

                                      And how does one know if the hardware supports automatic ADC gain and offset calibration?

                                      Again I have no idea but I suspect @dc42 would.

                                      Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

                                      Dougal1957undefined 1 Reply Last reply Reply Quote 0
                                      • Dougal1957undefined
                                        Dougal1957 @fcwilt
                                        last edited by

                                        @fcwilt I do use PT1000 and 100's as well and do prefer them and don't have any need for the additional Params as yet but we will see Hopefully Kevin gets it all sorted

                                        fcwiltundefined 1 Reply Last reply Reply Quote 1
                                        • fcwiltundefined
                                          fcwilt @Dougal1957
                                          last edited by

                                          @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                                          @fcwilt I do use PT1000 and 100's as well and do prefer them and don't have any need for the additional Params as yet but we will see Hopefully Kevin gets it all sorted

                                          Do those devices require additional hardware to connect to a Duet board?

                                          Frederick

                                          Printers: a small Utilmaker style, a small CoreXY and a E3D MS/TC setup. Various hotends. Using Duet 3 hardware running 3.4.6

                                          Dougal1957undefined KevinMarundefined DIY-O-Sphereundefined 3 Replies Last reply Reply Quote 0
                                          • Dougal1957undefined
                                            Dougal1957 @fcwilt
                                            last edited by

                                            @fcwilt said in Tool Board Heater Tuning Leading To Faults:

                                            @dougal1957 said in Tool Board Heater Tuning Leading To Faults:

                                            @fcwilt I do use PT1000 and 100's as well and do prefer them and don't have any need for the additional Params as yet but we will see Hopefully Kevin gets it all sorted

                                            Do those devices require additional hardware to connect to a Duet board?

                                            Frederick

                                            pt1000 no but the pt100 does need the daughter board