      KevinMar @dc42
      last edited by

      @dc42 C values changed when tuning with the sock.

      R values were a manual change

      dc42undefined 1 Reply Last reply Reply Quote 0
      • KevinMarundefined
        KevinMar @fcwilt
        last edited by

        @fcwilt "Print will be terminated if a heater fault is not reset within 10 minutes"

        fcwiltundefined 1 Reply Last reply Reply Quote 1
        • dc42undefined
          dc42 administrators @KevinMar
          last edited by

          @kevinmar confirm you are running firmware 3.3 on both main board and tool board?

          Duet WiFi hardware designer and firmware engineer
          Please do not ask me for Duet support via PM or email, use the forum
          http://www.escher3d.com, https://miscsolutions.wordpress.com

          KevinMarundefined 1 Reply Last reply Reply Quote 0
          • KevinMarundefined
            KevinMar @dc42
            last edited by

            @dc42 yes, 100%. All running 3.3 non beta or anything

            1 Reply Last reply Reply Quote 0
            • fcwiltundefined
              fcwilt @KevinMar
              last edited by

              @kevinmar said in Tool Board Heater Tuning Leading To Faults:

              @fcwilt "Print will be terminated if a heater fault is not reset within 10 minutes"

              As a test have you commented out the settings for all but one tool heater to see if that makes a difference?

              Frederick

              Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

              KevinMarundefined 1 Reply Last reply Reply Quote 0
              • KevinMarundefined
                KevinMar @fcwilt
                last edited by

                @fcwilt huh? Just comment out all of the heaters? I have not tried that.

                Should I add "M570 H1 P10 T15 S0" to my config?

                fcwiltundefined 1 Reply Last reply Reply Quote 0
                • KevinMarundefined
                  KevinMar
                  last edited by

                  The thing that keeps confusing me is that this is a very standard-issue setup. Running all standard E3D + Duet hardware, and running a stable release of the firmware.

                  fcwiltundefined 1 Reply Last reply Reply Quote 1
                  • fcwiltundefined
                    fcwilt @KevinMar
                    last edited by fcwilt

                    @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                    @fcwilt huh? Just comment out all of the heaters? I have not tried that.

                    Should I add "M570 H1 P10 T15 S0" to my config?

                    I was wondering if the same problem would occur you if you only had one extruder heater configured.

                    As to the M570 I was working with out of date documentation.

                    It turns out with current firmware it appears you have to have a H parameter to set/report on a given heater.

                    Frederick

                    Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                    1 Reply Last reply Reply Quote 0
                    • fcwiltundefined
                      fcwilt @KevinMar
                      last edited by

                      @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                      The thing that keeps confusing me is that this is a very standard-issue setup. Running all standard E3D + Duet hardware, and running a stable release of the firmware.

                      It most certainly is confusing but I would not be surprised if we are overlooking something that should be obvious.

                      Frederick

                      Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                      KevinMarundefined 1 Reply Last reply Reply Quote 0
                      • KevinMarundefined
                        KevinMar @fcwilt
                        last edited by

                        @fcwilt Me too, but I've been digging

                        KevinMarundefined fcwiltundefined 2 Replies Last reply Reply Quote 0
                        • KevinMarundefined
                          KevinMar @KevinMar
                          last edited by

                          This post is deleted!
                          1 Reply Last reply Reply Quote 0
                          • fcwiltundefined
                            fcwilt @KevinMar
                            last edited by

                            @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                            @fcwilt Me too, but I've been digging

                            When I'm faced with something like this I resort to a process of elimination, thus my suggestion to configure just one heater to see if it changes anything.

                            Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                            KevinMarundefined 1 Reply Last reply Reply Quote 0
                            • KevinMarundefined
                              KevinMar @fcwilt
                              last edited by

                              @fcwilt I've commented out all heaters except H2, autotuning now.
                              "M308 S2 P"21.temp0" Y"pt1000" A"Ex1"
                              M950 H2 C"21.out0" T2 ; Heater for extruder out tool 1
                              M307 H2 R2.050 C309.100:130.600 D6.20 S1.00 V24.3 B0
                              M570 H2 P10 T25 S0.1"

                              fcwiltundefined 1 Reply Last reply Reply Quote 0
                              • fcwiltundefined
                                fcwilt @KevinMar
                                last edited by

                                @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                                @fcwilt I've commented out all heaters except H2, autotuning now.
                                "M308 S2 P"21.temp0" Y"pt1000" A"Ex1"
                                M950 H2 C"21.out0" T2 ; Heater for extruder out tool 1
                                M307 H2 R2.050 C309.100:130.600 D6.20 S1.00 V24.3 B0
                                M570 H2 P10 T25 S0.1"

                                Worth a try.

                                At some point did you verify that each tool board is actually at the address you are using?

                                Frederick

                                Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                                KevinMarundefined 1 Reply Last reply Reply Quote 0
                                • KevinMarundefined
                                  KevinMar @fcwilt
                                  last edited by

                                  @fcwilt Yes, toolboards are at the addresses assigned

                                  fcwiltundefined 1 Reply Last reply Reply Quote 1
                                  • Phaedruxundefined
                                    Phaedrux Moderator
                                    last edited by

                                    Can you send M98 P"config.g" to check for any syntax errors?

                                    I'd also suggest generating a basic config using the online tool and trying with that.

                                    Perhaps a photo of the hotend itself my give us some clues.

                                    Z-Bot CoreXY Build | Thingiverse Profile

                                    1 Reply Last reply Reply Quote 0
                                    • fcwiltundefined
                                      fcwilt @KevinMar
                                      last edited by

                                      @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                                      @fcwilt Yes, toolboards are at the addresses assigned

                                      I've got a test setup on my workbench but it only has one tool board connected and it works fine.

                                      Perhaps there is some as yet undiscovered firmware problem that only manifests with multiple tool boards.

                                      Frederick

                                      Printers: a E3D MS/TC setup and a RatRig Hybrid. Using Duet 3 hardware running 3.4.6

                                      KevinMarundefined 1 Reply Last reply Reply Quote 0
                                      • KevinMarundefined
                                        KevinMar @fcwilt
                                        last edited by

                                        @fcwilt @dc42
                                        Here's my new, super simple config

                                        M550 P"ToolChanger" 					; Set machine name
                                        M111 S0                              	; Debug off
                                        M929 P"eventlog.txt" S1					; Start logging to file eventlog.txt
                                        M555 P1									; Set RepRap output
                                        
                                        G4 S1  									; Wait for expansion boards to start
                                        
                                        
                                        M308 S2 P"21.temp0" Y"pt1000"  A"Ex1"  
                                        
                                        M950 H2 C"21.out0" T2						; Heater for extruder out tool 1
                                        
                                        
                                        M307 H2 R2.063 C316.300:132.500 D6.10 S1.00 V24.3 B0
                                        
                                        
                                        M143 H2 S300
                                        
                                        M950 F11 C"21.out2"
                                        M106 P11 S255 H2 T70
                                        
                                        
                                        M950 F1 C"21.out1"
                                        
                                        
                                        M563 P1 S"Tool1"  H2 F1
                                        G10  P1 S220 R205
                                        
                                        M570 H2 P10 T25 S0.1
                                        
                                        G29 S2
                                        T-1
                                        
                                        M501									; Load config-override.g
                                        
                                        KevinMarundefined Phaedruxundefined 2 Replies Last reply Reply Quote 0
                                        • KevinMarundefined
                                          KevinMar @KevinMar
                                          last edited by KevinMar

                                          boom, fault at 70c

                                          It's most commonly faulting at 70c, which is when my hotend cooling fan is enabled

                                          fcwiltundefined 1 Reply Last reply Reply Quote 0
                                          • Phaedruxundefined
                                            Phaedrux Moderator @KevinMar
                                            last edited by

                                            @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                                            M307 H2 R2.063 C316.300:132.500 D6.10 S1.00 V24.3 B0

                                            @kevinmar said in Tool Board Heater Tuning Leading To Faults:

                                                                                                                                                                                                                    M501									; Load config-override.g
                                            

                                            Does that M307 line match what gets loaded by config-override?

                                            Z-Bot CoreXY Build | Thingiverse Profile

                                            KevinMarundefined 1 Reply Last reply Reply Quote 0