    Feature Request - workpiece angle compensation CNC
    Firmware wishlist
    11
    54
    2.7k
    • CanDo415undefined
      CanDo415 @jay_s_uk
      @jay_s_uk
      @Phaedrux
      Error: line 37 column 22: meta command: unknown value 'degrees'
      there seems to be a bit more
        jay_s_uk @CanDo415
        @CanDo415 i've made another change but I don't think its going to fix the issue.
        I don't know why "degrees" throws an error though as its a built in command
        CanDo415undefined OwenDundefined 2 Replies Last reply Reply Quote 0
        • CanDo415undefined
          CanDo415 @jay_s_uk
          that's why i added Phaedrux.
          I want to change it a bit to get the corner as well. so the degrees issue has to be solved anyway.
          Thanks for the great start jay
          CanDo415undefined 1 Reply Last reply Reply Quote 0
          • CanDo415undefined
            CanDo415 @CanDo415
            maybe he can help?
              droftarts administrators @CanDo415
              @CanDo415 @jay_s_uk
              set var.var y_x_tan_rads=degrees{var.y_x_tan_rads}
              There's a space in the variable name, ie var.var y_x_tan_rads isn't a valid variable name.
              • CanDo415undefined
                CanDo415 @droftarts
                @droftarts
                jay corrected it already.
                the problem shifted to the degrees command
                • OwenDundefined
                  OwenD @jay_s_uk
                  @jay_s_uk said in Feature Request - workpiece angle compensation CNC:
                  degrees() is a function
                  You've used curly braces instead of parentheses
                  set var.y_x_tan_deg=degrees{var.y_x_tan_rads}
                  try
                  set var.y_x_tan_deg=degrees(var.y_x_tan_rads)
                  jay_s_ukundefined CanDo415undefined 2 Replies Last reply Reply Quote 2
                    jay_s_uk @OwenD
                    @OwenD i knew it would be something about the way its been formatted
                    updated the original again
                    • CanDo415undefined
                      CanDo415 @OwenD
                      @OwenD
                      thank you for showing up the problem
                      • CanDo415undefined
                        CanDo415 @CanDo415
                        G68 A0 B0 R{-var.y_x_tan_rads}
                        the "-" seems important. otherwise the system gets turned the wrong way round
                        • CanDo415undefined
                          CanDo415 @CanDo415
                          @jay_s_uk
                          i modified it quite a bit. some points are still not ready.
                          I'm not shure how to ent the if passage.
                          end if seems not to work
                          var y_1 = 0
                          var x_1 = 0
                          var x_2 = 0
                          var x_3 = 0
                          var x_4 = 0
                          var x_5 = 0
                          var delta_x = 0
                          var y_2 = 0
                          var y_3 = 0
                          var y_4 = 0
                          var y_5 = 0
                          var delta_y = 0
                          var z0 = 0
                          var d_probe = 0
                          var m_1 = 0
                          var m_2 = 0
                          var m_1_tan_rads = 0
                          var m_1_tan_deg = 0
                          M291 P"position probe over front left corner of workpiece" S2 X1 Y1 Z1	; Pop up box asking for operator input
                          M558 F300																		; Set the initial probing speed
                          G38.2 Z-60 P0 K0																; Probe the material as a first pass
                          M558 F50																		; Set the final probing speed
                          G38.4 Z50 P0 K0        ; Move away from workpiece in Z
                          M400																			        ; Make sure all movement is complete
                          set var.z0=move.axes[2].machinePosition	                			    		                ; Record the stop position y_first_measurement
                          M400																			        ; Make sure all data recording is complete
                          G1 Z{move.axes[2].machinePosition+5}										; Move along the workpiece in X
                          G1 X{move.axes[0].machinePosition-20}										; Move 5mm away from the material
                          G1 Y{move.axes[1].machinePosition+5}										; Move 5mm away from the material
                          G1 Z{move.axes[2].machinePosition-3}											; Move along the workpiece in X
                          M558 F1000																		; Set the initial probing speed
                          G38.2 X100 P0 K0																; Probe the material as a first pass
                          G38.4 X-10 P0 K0        ; Move away from workpiece in X
                          set var.y_1=move.axes[1].machinePosition							    		        ; Record the stop position y_first_measurement
                          set var.x_1=move.axes[0].machinePosition							    		        ; Record the stop position x_first_measurement
                          G1 X{move.axes[0].machinePosition-5}											; Move 5mm away from the material
                          G1 Z{move.axes[2].machinePosition+10}										; Move along the workpiece in X
                          G1 X{move.axes[0].machinePosition+15}										; Move 5mm away from the material
                          G1 Y{move.axes[1].machinePosition-20}										; Move 5mm away from the material
                          G1 Z{move.axes[2].machinePosition}	    										; Move along the workpiece in X
                          G38.2 Y100 P0 K0																; Probe the material as a first pass
                          G38.4 Y-10 P0 K0															        ; Probe the material again
                          set var.y_2=move.axes[1].machinePosition								    	        ; Record the stop position y_first_measurement
                          set var.x_2=move.axes[0].machinePosition					    				        ; Record the stop position x_first_measurement
                          G1 Y{move.axes[1].machinePosition-50}										; Move 5mm away from the material
                          G1 X{move.axes[0].machinePosition+50}										; Move along the workpiece in X
                          set var.y_3=move.axes[1].machinePosition								    	        ; Record the stop position y_second_measurement
                          set var.x_3=move.axes[0].machinePosition								    	        ; Record the stop position x_second_measurement
                          M291 P"Probe Diameter" R"enter diameter of probe" S5 L0 H10			; Pop up box asking for operator input diameter of
                          set var.d_probe=input															; set the diameter of the probe
                          ;calculation
                          set var.delta_y={var.y_3-var.y_2}
                          set var.delta_x={var.x_3-var.x_2}
                          set var.m_1={var.delta_y/var.delta_x}											; m of the staight P2-P3
                          set var.m_2={(-var.delta_x)/var.delta_y}										        ; m of perpendicilar to straight P2-P3
                          set var.m_1_tan_rads=atan(var.m_1)
                          set var.m_1_tan_deg=degrees(var.m_1_tan_rads)
                          ;calc the corner of workpeace
                          set var.x_4=((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))
                          set var.y_4=(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))+(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)
                          If var.y_2>var.y_3																; workpiece Zero coordinates
                          set var.x_5=var.x_4+(COS(ARCTAN(var.m_1))+COS(ARCTAN(var.m_2)))*var.d_probe/2
                          set var.y_5=var.y_4+(SIN(ARCTAN(var.m_1))+SIN(ARCTAN(var.m_2)))*var.d_probe/2
                          If var.y_2<var.y_3
                          set var.x_5=var.x_4+(COS(ARCTAN(var.m_1))-COS(ARCTAN(var.m_2)))*var.d_probe/2
                          set var.y_5=var.y_4+(SIN(ARCTAN(var.m_1))-SIN(ARCTAN(var.m_2)))*var.d_probe/2
                          ;move over workpiece zero and set tool x&y to 0
                          G1 Y{move.axes[1].machinePosition-1}											        ; Move 1mm away from the material
                          G1 Z{move.axes[2].machinePosition+10}											; Move above workpiece
                          ;G68 A0 B0 R{-var.m_1_tan_deg}        ; set Rotation
                          Exerqtorundefined 1 Reply Last reply Reply Quote 0
                          • Exerqtorundefined
                            Exerqtor @CanDo415
                            @CanDo415
                            You have to indent the lines you want to be part of the conditional statement, thats a place to start at least.
                            • CanDo415undefined
                              CanDo415 @Exerqtor
                              @Exerqtor
                              like:
                              end if
                              If var.y_2<var.y_3
                              end if
                              Exerqtorundefined dc42undefined 2 Replies Last reply Reply Quote 0
                              • Exerqtorundefined
                                Exerqtor @CanDo415
                                @CanDo415
                                No like:
                                if var.y_2 > var.y_3																; workpiece Zero coordinates
                                  set var.x_5 = var.x_4 + (COS(ARCTAN(var.m_1)) + COS(ARCTAN(var.m_2))) * var.d_probe / 2
                                  set var.y_5 = var.y_4 + (SIN(ARCTAN(var.m_1)) + SIN(ARCTAN(var.m_2))) * var.d_probe / 2
                                if var.y_2 < var.y_3
                                  set var.x_5 = var.x_4 + (COS(ARCTAN(var.m_1)) - COS(ARCTAN(var.m_2))) * var.d_probe / 2
                                  set var.y_5 = var.y_4 + (SIN(ARCTAN(var.m_1)) - SIN(ARCTAN(var.m_2))) * var.d_probe / 2
                                • CanDo415undefined
                                  CanDo415 @Exerqtor
                                  @Exerqtor
                                  i tried this before in another case... everything unter the 2nd if wasnt done if the if doesn't match.
                                  the problem of the missing end if
                                  Exerqtorundefined jay_s_ukundefined 2 Replies Last reply Reply Quote 0
                                  • Exerqtorundefined
                                    Exerqtor @CanDo415
                                    @CanDo415
                                    Then you simply must have done something wrong in the other case you're mentioning.
                                    As reference to conditional construct have look at this.
                                      jay_s_uk @CanDo415
                                      @CanDo415 as @Exerqtor said, there's no end if.
                                      Things have to be indented to be part of the if
                                        dc42 administrators @CanDo415
                                        @CanDo415 you also need to replace SIN by sin, COS by cos, ARCTAN by atan etc. See https://docs.duet3d.com/User_manual/Reference/Gcode_meta_commands#functions.
                                        CanDo415undefined 1 Reply Last reply Reply Quote 1
                                        • CanDo415undefined
                                          CanDo415 @dc42
                                          thanks so far.
                                          Error promt is:
                                          M292 S3
                                          Error: Bad command: If (var.y_2) >= (var.y_3)
                                          Error: in file macro line 179 column 8: meta command: expected "'"
                                          Makro:
                                          G68 A0 B0 R0
                                          var y_1 = 0
                                          var x_1 = 0
                                          var x_2 = 0
                                          var x_3 = 0
                                          var x_4 = 0
                                          var x_5 = 0
                                          var delta_x = 0
                                          var y_2 = 0
                                          var y_3 = 0
                                          var y_4 = 0
                                          var y_5 = 0
                                          var delta_y = 0
                                          var z0 = 0
                                          var d_probe = 0
                                          var z_probe = 0
                                          var m_1 = 0
                                          var m_2 = 0
                                          var m_1_rads = 0
                                          var m_1_deg = 0
                                          var buff1 = 0
                                          var buff2 = 0
                                          var buff3 = 0
                                          var speed = 1500
                                          M291 P"probe Diameter" R"enter diameter of probe" S5 							; Pop up box asking for operator input diameter of
                                          set var.d_probe = input															; set the diameter of the probe
                                          M291 P"probe size in z" R"enter z-size of probe" S5 							; Pop up box asking for operator input diameter of
                                          set var.z_probe = input															; set the size of the probe in z-direction (mostly same as diameter, for plate probes 0)
                                          M558 F{var.speed/5}																; Set the initial movement speed
                                          G38.2 Z-10 P0 K0																; Probe the material on top
                                          set var.z0 = move.axes[2].machinePosition										; Record the stop position z_first_measurement
                                          G1 Z{move.axes[2].machinePosition+5}											; Lift probe 5mm
                                          G1 X{move.axes[0].machinePosition-20} Y{move.axes[1].machinePosition+5}			; Move 20mm to the left of the initial point and 5mm deeper into the material direction
                                          G1 Z{var.z0 - 1 - var.z_probe / 2}												; Move to probe depth
                                          M558 F{var.speed}																; Set the initial movement speed
                                          G38.2 X1000 P0 K0																; Probe the material as a first pass
                                          set var.y_1 = move.axes[1].machinePosition										; Record the stop position y_first_measurement
                                          set var.x_1 = move.axes[0].machinePosition										; Record the stop position x_first_measurement
                                          G1 Z{var.z0+5}																	; Move 5mm above material
                                          G1 X{move.axes[0].machinePosition+15} Y{move.axes[1].machinePosition-20}		; Move to point 2
                                          G38.2 Y1000 P0 K0																; Probe the material as a first pass
                                          set var.y_2 = move.axes[1].machinePosition										; Record the stop position y_second_measurement
                                          set var.x_2 = move.axes[0].machinePosition										; Record the stop position x_second_measurement
                                          G1 Y{move.axes[1].machinePosition-20}											; Move 10mm away from the material
                                          G1 X{move.axes[0].machinePosition+50}											; Move 50mm along the workpiece in X
                                          set var.y_3 = move.axes[1].machinePosition										; Record the stop position y_third_measurement
                                          set var.x_3 = move.axes[0].machinePosition										; Record the stop position x_third_measurement
                                          ;calculation
                                          set var.delta_y = {var.y_3-var.y_2}
                                          set var.delta_x = {var.x_3-var.x_2}
                                          set var.m_1 = {var.delta_y/var.delta_x}											; m of the staight P2-P3
                                          set var.m_2 = {(-var.delta_x)/var.delta_y}										; m of perpendicilar to straight P2-P3
                                          set var.m_1_rads = atan(var.m_1)												; workpiece rotation in rad
                                          set var.m_1_deg = degrees(var.m_1_rads)											; workpiece rotation in degrees
                                          ;calc the corner of workpiece
                                          ;set var.x_4 = {((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))}
                                          ;set var.y_4 = {(-(var.x_3-var.x_2)/(var.y_3-var.y_2))<>*((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))<>/(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))+(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)}
                                          set var.buff1 = {var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1}
                                          set var.buff2 = {var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)}
                                          set var.buff3 = {((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))}
                                          set var.x_4 = {(var.buff1-var.buff2)/var.buff3}
                                          set var.buff1 = {(-(var.x_3-var.x_2)/(var.y_3-var.y_2))}
                                          set var.buff2 = {((var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)-(var.y_2-((var.y_3-var.y_2)/(var.x_3-var.x_2)*var.x_2)))}
                                          set var.buff3 = {(((var.y_3-var.y_2)/(var.x_3-var.x_2))-(-(var.x_3-var.x_2)/(var.y_3-var.y_2)))+(var.y_1-(-(var.x_3-var.x_2)/(var.y_3-var.y_2))*var.x_1)}
                                          set var.y_4 = {var.buff1*var.buff2/var.buff3}
                                          If (var.y_2) >= (var.y_3)																; workpiece Zero coordinates
                                          set var.x_5 = {var.x_4+(cos(atan(var.m_1))+cos(atan(var.m_2)))*var.d_probe/2}
                                          set var.y_5 = {var.y_4+(sin(atan(var.m_1))+sin(atan(var.m_2)))*var.d_probe/2}
                                          echo 'X= '{var.x_5}', Y= '{var.y_5}
                                          If (var.y_2) < (var.y_3)
                                          set var.x_5 = {var.x_4+(cos(atan(var.m_1))-cos(atan(var.m_2)))*var.d_probe/2}
                                          set var.y_5 = {var.y_4+(sin(atan(var.m_1))-sin(atan(var.m_2)))*var.d_probe/2}
                                          ;echo X= {var.x_5}, Y= {var.y_5}
                                          ;move above workpiece zero and set tool x&y to 0
                                          G1 Z{var.z0 + 5}																; Move above workpiece
                                          G1 X{var.x_5} Y{var.y_5}														; go to Zero
                                          G10 X0 Y0																		; set x&y to Zero
                                          G68 A0 B0 R{-var.m_1_deg}														; set Rotation
                                          X seems to be working, on a psitive angle.
                                          Y is getting some wrong outputs
                                            @CanDo415 replace all If by if.